Hello all, i have a question on selection of circuit breaker.
Can 4P 125A 16kA breaker be used in place of 4P 125A 10kA ?
I appreciate your sincere response.
 

·
Registered
Joined
·
3 Posts
Discussion Starter #3
Hello Rahmon:thumbsup:
I do not think so, You should use the exact same make and model number.
Thank you for the answer.
perhaps I'm not clear with " You should use the exact same make and model number"
But I like to state that what is required is 4P 125A 10kA circuit breaker, but that particular kind of breaker with such features is obsolete and I am now thinking of possible substitute.
 

·
Electrical Simpleton
Joined
·
3,350 Posts
That's a difficult question to give a "yes" or "no" answer to without more information.

Is the 10kA rated breaker you are looking to replace part of a series rated combination?

Is the available fault current at or below 10,000 amps?

Is the replacement breaker recognized for use in the equipment?

Pete
 
  • Like
Reactions: Rahmon

·
Banned
Joined
·
11,766 Posts
Hello all, i have a question on selection of circuit breaker.
Can 4P 125A 16kA breaker be used in place of 4P 125A 10kA ?
I appreciate your sincere response.
You need to know your available fault current (do you have a tester?) for both line-line and line-PE faults.
 