Discussion Starter · #1 ·
Bidding on a 64x40 pole building..
-Trench 170' to customers pole and install 4/0 URD in 2 1/2 pvc, U-guard up the pole, mini ex rental is 200 a day and backfill
-Install 200 AMP SQD disconnect on outside
-Install 200 amp QO 30/40 panel
-Run 10/2 100 feet for Air Compressor Circuit
-10 Outlets mounted on beams ( run Emt to ceiling than with 12-2 romex
-Install 8 T5 6 lamp fixtures (customer supplying)
-Install (3) 100 Watt MH wallpacks
-NO water, so installing 2 ground rods
-Run 6-2 115' for welder circuit
-The building is attached to the old shop so im running 100 amp SER to to power the old building (Roughly 85')

Supply all materials except lights.
 

· RIP 1959-2015
Joined
·
39,532 Posts
Bidding on a 64x40 pole building..
-Trench 170' to customers pole and install 4/0 URD in 2 1/2 pvc, U-guard up the pole, mini ex rental is 200 a day and backfill
-Install 200 AMP SQD disconnect on outside
-Install 200 amp QO 30/40 panel
-Run 10/2 100 feet for Air Compressor Circuit
-10 Outlets mounted on beams ( run Emt to ceiling than with 12-2 romex
-Install 8 T5 6 lamp fixtures (customer supplying)
-Install (3) 100 Watt MH wallpacks
-NO water, so installing 2 ground rods
-Run 6-2 115' for welder circuit
-The building is attached to the old shop so im running 100 amp SER to to power the old building (Roughly 85')

Supply all materials except lights.
$64,749.03.:thumbsup:
 

· Registered
Joined
·
928 Posts
Bidding on a 64x40 pole building..
-Trench 170' to customers pole and install 4/0 URD in 2 1/2 pvc, U-guard up the pole, mini ex rental is 200 a day and backfill
-Install 200 AMP SQD disconnect on outside
-Install 200 amp QO 30/40 panel
-Run 10/2 100 feet for Air Compressor Circuit
-10 Outlets mounted on beams ( run Emt to ceiling than with 12-2 romex
-Install 8 T5 6 lamp fixtures (customer supplying)
-Install (3) 100 Watt MH wallpacks
-NO water, so installing 2 ground rods
-Run 6-2 115' for welder circuit
-The building is attached to the old shop so im running 100 amp SER to to power the old building (Roughly 85')

Supply all materials except lights.
Do you already have the job? What was your price?
 

· :-)
Joined
·
3,664 Posts
Are you sub contracting this out? I'm beating Harry...

$64,549.03

25K up front. the rest to be determined.

Anyway write down all your material including screws, etc. Put a price and a labor unit to each item. A switch plate might take .01 hr. to install type of thing.

Add a bunch of stuff to account for office, truck, utilities expense, etc.

You are good to go.
 

· Registered
Joined
·
385 Posts
Nevermind, just noticed you're an apprentice. Is all the material supplied? If not you won't make a dime on this one. If so you will make apprentice wages doing it. What about permit? Why are you bidding a job like this as an apprentice?
 

· Retired Account
Joined
·
39,616 Posts
Bidding on a 64x40 pole building..


-Trench 170' to customers pole and install 4/0 URD in 2 1/2 pvc, U-guard up the pole, mini ex rental is 200 a day and backfill
-Install 200 AMP SQD disconnect on outside
-Install 200 amp QO 30/40 panel
$5k & rental


-Run 10/2 100 feet for Air Compressor Circuit
$400

-10 Outlets mounted on beams ( run Emt to ceiling than with 12-2 romex
$200 ea & manlift =$2000

-Install 8 T5 6 lamp fixtures (customer supplying)
$300 ea = $2400

-Install (3) 100 Watt MH wallpacks
$300ea =$900

-NO water, so installing 2 ground rods
include in service $

-Run 6-2 115' for welder circuit
$500

-The building is attached to the old shop so im running 100 amp SER to to power the old building (Roughly 85')
$500, terminates in whatever they have, if not kosher cost +

Supply all materials except lights.
Note listing/rating required for area, no warranty, not liable for any AHJ interaction / judgements

Permits pulled & ins. voucher forwarded with signatures and 1/3 down, consummate progress payments

$11,700 + digger and manlift rental charged on a daily basis (i.e.- if weather, your cows, or anything else you conjure up impedes the job, it's on you!)

~CS~
 