60 ckt QO ordered yesterday. And it will be sideways.
The NEC has a requirement that won't allow a breaker handle to be down in the on position. So a sideways mounted panel would only be allowed to use the bottom spaces because any breaker on the top would have the handle down in the on position and that would be a code violation.

Does the Canadian code not have that requirement?
 

·
Moderator
Estwing magic
Joined
·
27,292 Posts
The NEC has a requirement that won't allow a breaker handle to be down in the on position. So a sideways mounted panel would only be allowed to use the bottom spaces because any breaker on the top would have the handle down in the on position and that would be a code violation.

Does the Canadian code not have that requirement?
Nope and it drives you guys bonkers :) .

This comes from Square D, for example:

"CSA approved for vertical, horizontal or inverted mounting and suitable for Al/Cu conductors"
 

·
Moderator
Estwing magic
Joined
·
27,292 Posts
There is a practical reason for it. Canadian panels, as far as I know, are different than yours'. The main breaker area is barriered. It makes an 80 circuit panel very long. With the main breaker at eye height, the lowest breaker is down at your knees. If the panel is mounted horizontally, all the breakers are at eye height. Highest breaker according to code should be at 5'6" (I did the metric conversion for you).
 

·
Registered
Joined
·
3,838 Posts
There is a practical reason for it. Canadian panels, as far as I know, are different than yours'. The main breaker area is barriered. It makes an 80 circuit panel very long. With the main breaker at eye height, the lowest breaker is down at your knees. If the panel is mounted horizontally, all the breakers are at eye height. Highest breaker according to code should be at 5'6" (I did the metric conversion for you).
Is it also correct that you cannot pass the branch circuit conductors through the main breaker area if that breaker is the service disconnect?

As far as the 5'6, are you guys shorter than us?...our maximum height to the center of the breaker handle is 2 meters, it was 6'6" before we added the metric measurements.
 

·
Electrical Contractor
Joined
·
9,325 Posts
Is it also correct that you cannot pass the branch circuit conductors through the main breaker area if that breaker is the service disconnect?

As far as the 5'6, are you guys shorter than us?...our maximum height to the center of the breaker handle is 2 meters, it was 6'6" before we added the metric measurements.
A 60 circuit panel installed recessed would be an interesting picture.
 