Joined
·
113 Posts
I was taught the cold water main needs to be bonded within 5' of entering a home, and that the water heater needs to be bonded around separately and run back to the panel. I am looking throughout 250 and can't find either of those requirements, only that the cold water needs to be bonded somewhere and the other pipes can be bonded to one of the grounding electrodes, not necessarily back to the disconnect.
So what I'm understanding is that you can bond the CW wherever is most convenient to tie into it, and then bond around the water heater, saying that the CW line is a grounding electrode (since the lateral is buried for over 10') and therefore you don't need to bring the water heater bonding line back to the panel.
Am I wrong?
So what I'm understanding is that you can bond the CW wherever is most convenient to tie into it, and then bond around the water heater, saying that the CW line is a grounding electrode (since the lateral is buried for over 10') and therefore you don't need to bring the water heater bonding line back to the panel.
Am I wrong?