I just partially rewired someone's garage. They had some NMB cable running through a piece of EMT that wasn't connected to anything else. I am thinking I need to bond this piece of pipe. (It goes overhead to another garage behind the one I rewired. Gotta love the maintenance man.) Anyway, I am hoping I can just put a ground clamp on that piece of pipe and hook it to a ground wire in the closest electrical box. (The garage is powered by one 15A multiwire circuit.) I remember reading something about having to bond both ends of the pipe but I have no idea whether that was just a discussion or if it is somewhere in the code book.
 

· RIP 1959-2015
Joined
·
39,532 Posts
I just partially rewired someone's garage. They had some NMB cable running through a piece of EMT that wasn't connected to anything else. I am thinking I need to bond this piece of pipe. (It goes overhead to another garage behind the one I rewired. Gotta love the maintenance man.) Anyway, I am hoping I can just put a ground clamp on that piece of pipe and hook it to a ground wire in the closest electrical box. (The garage is powered by one 15A multiwire circuit.) I remember reading something about having to bond both ends of the pipe but I have no idea whether that was just a discussion or if it is somewhere in the code book.
Read, 250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).
 

· Registered
Joined
·
347 Posts
Discussion Starter · #13 ·
I'll check that out when I get home (250)... there's a 7 foot piece of conduit going between the buildings and I ran uf wire through the conduit... it is only a sleeve and I'm getting the impression that a sleeve does not need to be bonded... I hope I have this correct.
 
1 - 15 of 15 Posts
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.
Top