Discussion Starter · #1 ·
Got boxes with 3# 8 grounds and 3# 10's. Anybody see an issue with crimping ring terminals on them and putting them under a long ground screw.
 

·
Registered
Joined
·
1,144 Posts
Got boxes with 3# 8 grounds and 3# 10's. Anybody see an issue with crimping ring terminals on them and putting them under a long ground screw.
IMO you are splicing conductors. This method isn't an option under 110.14,
e.g. it is not a splicing device identified for the use.
 

·
Registered
Joined
·
6,189 Posts
Is it a listed method if you use ring terminals and use a 1/4x20 bolt and but? Its done all the time.
 