Electrician Talk banner
1 - 3 of 3 Posts

·
Registered
Joined
·
1,867 Posts
Discussion Starter · #1 ·
So a 20Kw Generator is 83A @ 240v, a 8000w Generator is 33A @ 240v. I take it these amp ratings should be the breaker size for the Generator. So a 30A generator panel for an 8000w generator. Does the 80% rule apply to generators as well? I heard its 90%.
 

·
Registered
Joined
·
1,867 Posts
Discussion Starter · #4 ·
I've seen configurations where there's a 7000w-8000w generator feeding into a 60A emergency sub panel, I take it the 30A breaker built into these generators is what protects the generator and it doesn't matter that there's a 60A in the panel. The 60A is only acting as a switch at that point and working as a 60A breaker when in the utility position?

Hope I'm making myself clear lol
 
1 - 3 of 3 Posts
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.
Top