Discussion Starter · #1 ·
Anyone know the codes that govern accepted breaker ties. I've seen nails, 12g wire, etc. I know those aren't right.
 

·
Registered
Joined
·
13,403 Posts
Handle ties are in the 2020 code seven places. The word they use is identified.


Identified (as applied to equipment).



Recognizable as suitable for the specific purpose, function, use, environment, application, and so forth, where described in a particular Coderequirement. (CMP-1)
Informational Note:
Some examples of ways to determine suitability of equipment for a specific purpose, environment, or application include investigations by a qualified testing laboratory (listing and labeling), an inspection agency, or other organizations concerned with product evaluation.


Font Number Screenshot Parallel
 

·
Registered
Joined
·
2 Posts
Some (I won't say who) have suggested the only reason for a breaker handle tie is to make manual tripping of both ungrounded connectors necessary. They go on to say that because the nail, wire, whatever identifies the two legs of the circuit a manufacturer's tie isn't needed. Overload tripping of both circuits will not occur but that's OK.
 

·
Registered
Water treatment plant maintenance
Joined
·
756 Posts
I know we have a couple at the plant with a piece of gas welding rod through them. Code wise though you basically would have to buy them from the breaker manufacture listed for the specific breaker right ? Functionally I don't know if it matters...
 

·
Registered
Residential, lite comm., Industrial
Joined
·
1,167 Posts
Some (I won't say who) have suggested the only reason for a breaker handle tie is to make manual tripping of both ungrounded connectors necessary. They go on to say that because the nail, wire, whatever identifies the two legs of the circuit a manufacturer's tie isn't needed. Overload tripping of both circuits will not occur but that's OK.
I thought i remembered a code description of "common trip" for 220V breakers ?
 

·
Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
2,020 Posts
I don't think we need them period. If the job can't afford a 2-pole breaker, there's something wrong.
I agree but sometimes you get stuck on a job and you must improvise. New but defective breaker. Unexpected brand breaker. etc.... How many breakers can one keep in the truck? I try to keep 2 - double poles of the popular brands and sizes.
 

·
Registered
Install, troubleshoot, maintain, and upgrade electrical systems, plant utilities, PLC's, mechanical
Joined
·
587 Posts
This account is a bit of the opposite.
A couple of years ago I started with this company and the Maintenance supervisor is the only one that really knew my background.
Our Maintenance supervisor was out because he tested postive to the virus.
The Plant Manager is now "supervising".

Walked up on a conversation between the Plant manager and an electrical contractor they had used previously.
The only space left in the panel had a two pole 20 amp bolt-in breaker in it.
The contractor was explaining he would have to remove the 2 pole breaker and install two 1 pole breakers.
If he did it live, he would have to use arc flash gear and have to charge extra for "hazardous work".
If the panel was shutdown it would be safer and cost less.
OK, I'll agree with shutting down, but now you would need the production lines to be shutdown.
Both methods cost money.

I was asked what would I recommend?
This I said, and took out my tweeker screw driver, and popped the breaker tie piece off, there you are....2-1 pole breakers.

Contractor was PO'ed.

I really didn’t want this guy back in "MY" plant, he took advantage of the plant with some of his previous work, prior to my arrival.
He was hired to run power to five new exhaust fans in a warehouse expansion.
Five conduit runs, five roof disconnects, five 3 pole breakers.
What did he not install?
Five motor starters with overload protection.

I figure he took the company for about $5000.00 for the starters he didn't install.

Now after a storm that caused a loss of a phase, we have 5 rooftop exhaust fans with burnt out motors.
Also discovered the firestats were not wired up correctly, of course without a starter to wire them to, what do you do?
I know what you don't do.
He ran one phase of the 480 through the firestat which is only rated for 120.

Did I do the contractor wrong or did I do my employer right?

Plant manager was happy.
 

·
Registered
Industrial / controls
Joined
·
21 Posts
This account is a bit of the opposite.
A couple of years ago I started with this company and the Maintenance supervisor is the only one that really knew my background.
Our Maintenance supervisor was out because he tested postive to the virus.
The Plant Manager is now "supervising".

Walked up on a conversation between the Plant manager and an electrical contractor they had used previously.
The only space left in the panel had a two pole 20 amp bolt-in breaker in it.
The contractor was explaining he would have to remove the 2 pole breaker and install two 1 pole breakers.
If he did it live, he would have to use arc flash gear and have to charge extra for "hazardous work".
If the panel was shutdown it would be safer and cost less.
OK, I'll agree with shutting down, but now you would need the production lines to be shutdown.
Both methods cost money.

I was asked what would I recommend?
This I said, and took out my tweeker screw driver, and popped the breaker tie piece off, there you are....2-1 pole breakers.

Contractor was PO'ed.

I really didn’t want this guy back in "MY" plant, he took advantage of the plant with some of his previous work, prior to my arrival.
He was hired to run power to five new exhaust fans in a warehouse expansion.
Five conduit runs, five roof disconnects, five 3 pole breakers.
What did he not install?
Five motor starters with overload protection.

I figure he took the company for about $5000.00 for the starters he didn't install.

Now after a storm that caused a loss of a phase, we have 5 rooftop exhaust fans with burnt out motors.
Also discovered the firestats were not wired up correctly, of course without a starter to wire them to, what do you do?
I know what you don't do.
He ran one phase of the 480 through the firestat which is only rated for 120.

Did I do the contractor wrong or did I do my employer right?

Plant manager was happy.
You hate to hear it but it happens a lot. Obviously you did your employer right, **** that contractor.

Seems a lot of these plants have one of two approaches, they are totally hands off and let the contractors do what they want without competent inhouse guys to really verify their work, or they try to get involved in everything and penny pinch/micromanage every little 20$ part.
 

·
Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
2,020 Posts
A lot of places have pet outside contractor who rape the companies with high rates. I think there is something going under the table.
 

·
Registered
Install, troubleshoot, maintain, and upgrade electrical systems, plant utilities, PLC's, mechanical
Joined
·
587 Posts
The 2 pole breaker with the factory installed handle tie is almost certainly common trip. If one pole trips, the other will also trip.

But I think you did the right thing.
Most 2 pole breakers, depending on the design, with the handle tie removed will act as two separate breakers and will trip separately from one another.
A multi pole breaker with a single handle cannot be seperated.
 

·
Bilge Rat
motors and controls.........
Joined
·
8,897 Posts
Most 2 pole breakers, depending on the design, with the handle tie removed will act as two separate breakers and will trip separately from one another.
A multi pole breaker with a single handle cannot be seperated.
My experience has been that just about every factory made 2 pole is common trip, meaning that if one pole trips, the other will also.

It's not the handle tie that connects the 2 poles, it's an internal bar that you can't see.

With the handle tie removed, each pole can be manually turned on and off independent of the other but tripping is different.
 

·
Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
2,020 Posts
My experience has been that just about every factory made 2 pole is common trip, meaning that if one pole trips, the other will also.

It's not the handle tie that connects the 2 poles, it's an internal bar that you can't see.

With the handle tie removed, each pole can be manually turned on and off independent of the other but tripping is different.
I did not think that they were tied inside until I drilled the rivets and saw the trip mechanism between the two.
 