Electrician Talk banner
1 - 20 of 56 Posts

· Registered
Joined
·
16 Posts
Discussion Starter · #1 ·
Hi all: This job the customer wants everything by the book, using 200A AL/CU panel, Square D QO. All panels come with a lug torque label, but breaker ratings seem hard to find, a search f all CB specs showed nothing. Have 15...100A breakers. Anyone ever see a breaker torque spec? Anyone even use a torque wrench on panels or breakers? Many thanks! Jon Paul EE
 

· Banned
Joined
·
15,627 Posts
Hi all: This job the customer wants everything by the book, using 200A AL/CU panel, Square D QO. All panels come with a lug torque label, but breaker ratings seem hard to find, a search f all CB specs showed nothing. Have 15...100A breakers. Anyone ever see a breaker torque spec? Anyone even use a torque wrench on panels or breakers? Many thanks! Jon Paul EE
Sometimes main breaker torque specs are labeled on the panel.
 

· Registered
Joined
·
33,793 Posts
And 36 Inch Pounds is hardly anything, having torqued 20 amp QOB's to spec I can tell you 99.9% of connections on QOB's that are not torqued with a calibrated torque screwdriver are way over tightened.

This is one of several torque screw drivers our employees carry.

 

· Registered
Joined
·
33,793 Posts
In performing testing I have learned 90% of all electrical connections are over tightened, 9% torqued properly and 1% loose.

That was not data from a Gallop poll but me personal non-scientific WILD ASS GUESS and could be off as much as 100%.:laughing:. Actually I think for a guess it is close to accurate.
 

· Donuts > Fried Eggs
Joined
·
17,035 Posts
..In the past they offered $100 to anyone who could properly torque a 200A lug by feel.

Out of about 20 of us only one got it right but it wasn't me:mad:
Nuts, what was the tolerance, did it have to be dead-on to win?

I torque a ton of 1/2" bus-bar bolts and I can usually get within a couple foot-pounds by feel alone.
 

· Registered
Joined
·
3,106 Posts
Nuts, what was the tolerance, did it have to be dead-on to win?

I torque a ton of 1/2" bus-bar bolts and I can usually get within a couple foot-pounds by feel alone.
I think they quit doing it because of guys like you!:laughing:

They never said what the tolerance was. But they said they didn't give much money away.

In the Navy we had to torque some 3/4" nuts with a 2 ft wrench to 250 lb-ft. Usually we just hung on the wrench and it was good:laughing:
 

· Registered
Joined
·
448 Posts

· Registered
Joined
·
33,793 Posts
Document libraries that are disorganised, disjointed, hard to find, and obscure are sadly not just limited to Schneider.
It is a universal characteristic of all electrical manufacturers.
You will never make it testing circuit breakers, I have to have a manufactures brochure for every circuit breaker we test and we have to read them some are ridiculously long and disjointed. In this day and age it is a lot easier to obtain the data than in pre-internet days.
 

· Electrical Contractor
Joined
·
9,279 Posts
Most breakers with an Allen wrench bolt have the torque specs on them. Most of the SQ QO 200 amp stuff is 250 in lbs. We use a torque wrench all the time on larger breakers, CT cabinet lugs etc. POCO even looks at us a little funny but one split lug on a main breaker will buy you a number of torque wrenches.
 

· Registered
Joined
·
33,793 Posts
Most breakers with an Allen wrench bolt have the torque specs on them. Most of the SQ QO 200 amp stuff is 250 in lbs. We use a torque wrench all the time on larger breakers, CT cabinet lugs etc. POCO even looks at us a little funny but one split lug on a main breaker will buy you a number of torque wrenches.
If you are splitting lugs (NOT YOU PERSONALLY) you are not an electrician your a freaking gorilla.
 