ummm.......seriously?
Anyone ever heard of a rule about after a breaker trips once you have to replace it? This discussion came up at work.
I've heard this discussed here once. If the breaker is subject to high fault current aka a short circuit, I believe it's considered no longer reliable and should be replaced.Anyone ever heard of a rule about after a breaker trips once you have to replace it? This discussion came up at work.
This, though long term abuse at lower currents over time will cause the breaker to slowly degrade. And to elaborate the issue, remember these are mechanical devices the more you use em, the quicker they fail.I've heard this discussed here once. If the breaker is subject to high fault current aka a short circuit, I believe it's considered no longer reliable and should be replaced.
Yes I have.Anyone ever heard of a rule about after a breaker trips once you have to replace it? This discussion came up at work.
There is a reason for AIC ratings and that is to prevent an explosion of the breaker.Um, this seems absolutely ridiculous. What the hell good do breakers do that cheaper fuses can't? I think there is a reason why there are AIC ratings on breakers.
Breakers can handle the AIC and be able to reset and do it again, but UL only asks that they survive it 3 times under testing. After that its any bodies guess. Keep in mind that most commercial breakers are very close if not identical to the resi ones. All that really changes for the most part is the mounting arrangement and the arc shute/contact opening distance. Breakers where oout every time they are faulted even loaded near the trip rating. They are not fuses and require exercise and if you are talking large switchgear types one is supposed to maintain them along with testing. Breakers only really offer the convince of being reset, sometimes computer logic to and shunt trip. Other than that they are mediocre.Only under exceptional circumstances !
I think most times a breaker should be able to handle it !
Is the quality of electrical equipment really this poor ?
Do you know that or are you just guessing based on opinion?I've heard this discussed here once. If the breaker is subject to high fault current aka a short circuit, I believe it's considered no longer reliable and should be replaced.
That is what I am saying. They are operational even after a 10,000a event.There is a reason for AIC ratings and that is to prevent an explosion of the breaker.
Well that's what you get for having common sense and a bit of electrical knowledge. :thumbsup:I only throw in a main feeder breaker after everything upstream is opened.Shutdown, smallest to largest. Startup, largest to smallest is my M.O.
Agreed. UL 489 tests MCCBs to open and close three times into their full interrupting rating, after that, all bets are off.Under a bolted fault I would. Every bolted high current fault puts the contacts. And in truth a UL listed breaker is only guaranteed at 3 fully rated faults (I think if memory is correct)