Hi everyone; it's been awhile.
I hope everyone is having a nice New Year!
Got a service call because a main breaker was tripping instead of the branch circuit when a tenant was using a space heater. I overloaded the circuit to confirm and sure enough, the main breaker tripped, but NOT the branch circuit.
The main breaker was warm, but no burn marks/loose connections/burnt smell. I swapped it out. Fine.
I went upstairs and plugged (2) space heaters in the receptacle. After 5-10 mins, the branch circuit wouldn't trip.
So I swap the 20 Amp branch circuit breaker. Same thing; it didn't trip.
I put an amp meter on the line and sure enough, it's reading 24 Amps or so.
Has anyone seen anything like this? Is there a problem with QO breakers that anyone knows of?
It occurred to me that if the voltage was low, maybe the breaker wouldn't trip because the total WATTAGE would be lower even if the amperage was higher. What do you think?
Thanks for any thoughts.
Got a service call because a main breaker was tripping instead of the branch circuit when a tenant was using a space heater. I overloaded the circuit to confirm and sure enough, the main breaker tripped, but NOT the branch circuit.
The main breaker was warm, but no burn marks/loose connections/burnt smell. I swapped it out. Fine.
I went upstairs and plugged (2) space heaters in the receptacle. After 5-10 mins, the branch circuit wouldn't trip.
So I swap the 20 Amp branch circuit breaker. Same thing; it didn't trip.
I put an amp meter on the line and sure enough, it's reading 24 Amps or so.
Has anyone seen anything like this? Is there a problem with QO breakers that anyone knows of?
It occurred to me that if the voltage was low, maybe the breaker wouldn't trip because the total WATTAGE would be lower even if the amperage was higher. What do you think?
Thanks for any thoughts.