What loads are served by these cables?I have a situation where I have up to five NM 12 and 14 AWG cables bundled.
How do I show the inspector i have considered derating?
where there is 'space' i suppose.....Just what constitutes "maintaining spacing"?
What you say was very common here as well.where there is 'space' i suppose.....
here, land of manufactured zipper homes, we'll often receive them with two distinct bundles, each about 2" in diameter, one made made into the panel, the other with enough slack to reach the panel
Often the undersides of these units will simply extend a 2" hole , incorporating all wiring, to fan out as it becomes distal of the panel
two floor 'stackable zipper homes' incorporate a 2" sch 40 sleeve on either side, all the NM stuffed on in & down to the panel location
~CS~
In most cases the Exception to 310.15(A)(2) will permit bundling in the panel without derating.IMO this is a nightmare to enforce and really has never cause a problem in resi work, where the entire home pulls and average current of 30A, per some POCO's
Just what constitutes "maintaining spacing"?
Some folks ty-wrap/bundle conductors in panels for over 24" should they derate?
(3) Adjustment Factors. (a) More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600 mm (24 in.) and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown inTable 310.15(B)(3)(a).
Panel Statement: Section 310.15(B)(3)(a) is specific to conductors in raceway or cable. This section provides references to other sections, but contains rules for only conductors in raceways or cables.