I am doing a job for a customer in a strip mall and when we started demolition the power wasn’t hooked up. Upon firing up the unit panel and beginning to commission the existing electrical, I began finding all sorts of terrible wiring mistakes and bizarre electrical effects. Circuit loops, double feeds, shoddy connections, jam packed boxes, chattering contacts just to name a few You’ll never guess what the storefront used to be… a computer/phone repair shop! So it’s a classic case of “I can do this myself, I’m a computer guy”😂
I’ve managed to tear out all of the existing garbage while salvaging the home runs and useful whips to re-connect properly but there is one big problem; the panel feeds are severely under volted… it is a 3 phase 120/208v system and here are my measurements:
A: 120v
B: 55.5v
C: 65.5v
A-B: 176.4v
B-C: 9.4v
C-A:185.5v
Whatever is happening, it is upstream of the unit panel. Obviously this issue falls under the purview of the property manager, but my customer took the opportunity to highly recommend me to the strata company so now I have an email from them requesting my services, which I am luke warm on considering my current work load. What I think I am seeing in these numbers is a split phase between B and C. It’s like 120v is being divided between those two lugs and that’s why I’m only getting 10v between them. Makes me wonder why the computer store went out of business!
Anyways, what do you guys see happening here and what would the potential solution be? I just want a sounding board before I issue a work order and find myself tits deep in some ungodly mess! Thank you 🙏🏻
I’ve managed to tear out all of the existing garbage while salvaging the home runs and useful whips to re-connect properly but there is one big problem; the panel feeds are severely under volted… it is a 3 phase 120/208v system and here are my measurements:
A: 120v
B: 55.5v
C: 65.5v
A-B: 176.4v
B-C: 9.4v
C-A:185.5v
Whatever is happening, it is upstream of the unit panel. Obviously this issue falls under the purview of the property manager, but my customer took the opportunity to highly recommend me to the strata company so now I have an email from them requesting my services, which I am luke warm on considering my current work load. What I think I am seeing in these numbers is a split phase between B and C. It’s like 120v is being divided between those two lugs and that’s why I’m only getting 10v between them. Makes me wonder why the computer store went out of business!
Anyways, what do you guys see happening here and what would the potential solution be? I just want a sounding board before I issue a work order and find myself tits deep in some ungodly mess! Thank you 🙏🏻
Attachments
-
2.3 MB Views: 2
-
2.3 MB Views: 2
-
2.3 MB Views: 2