2-308
The space referred to in Subrule (1) shall be in addition to the space required for the operation of drawout-type equipment in either the connected, test, or fully disconnected position and shall be sufficient for the opening of enclosure doors and hinged panels to at least 90°.

Also don't get hung up on the 1 meter clearance. Table 56 changes that based on voltages.
 