CEC rules 4-004 and 4-006 de-rating

17374 Views 5 Replies 5 Participants Last post by  BlackHowling
rule 4-004 (14) makes sense as it is stated in the code. It compels us to avoid using wires with low temperature rating.
rule 4-006 rule is not offering any solutions, in case of long runs where it doesn’t make sense to run larger conductor just to keep a breaker happy.
rule 4-004 (1) and (2) (c) Four or more conductors in a conduit is wrong, including the table 5c.
It only works if all the conductors are the same size.
We can calculate resistance of conductors based on diameter. From the ampacity we can calculate the power (heat). From the volume and material of the raceway we can find a heat dissipation.
Aluminum rigid conduit will cool conductors significantly better than PVC conduit.

For an example a #12 AWG has 0.0055 Ohm/meter. At 10 A it dissipates 0.55W /m.
# 2 AWG has 0.00055 Ohm/m. At 100A it dissipates 5.5W/m.
A raceway with 9 wires #2 dissipate 50 Watt/meter.
A raceway with 3 wires #2AWG and 6 wires 12AWG dissipates 20 Watt/meter.
Both have to be de-rated by 0.7.
The raceway with mixed wire sizes is wrongly de-rated too much.
The rule and table also ignore the raceway material.
1 - 1 of 6 Posts
123 said:
. 4-006 When it comes to de-rating a 90 degree conductor because the circuit breaker is only 75 degree rated, the conductor has to be de-rated only at the connection to the breaker. The rest of the run is fine. I can splice the wires in a junction box 3 feet before the breaker and run larger conductor the last 3 feet. I would like to see the code allow running the conductor without de-rating, and find a way to cool the conductors before the breaker. like running larger conduit last couple of feet, or have a longer loop of the wire in the panel, before it’s connection.
There is a similar exception for motor circuits

28-104
(2) Where Table 37 requires insulation temperature ratings in excess of 75 °C, the motor supply conductors shall be not less than 1.2 m long and shall terminate in a location not less than 600 mm from any part of the motor except that for motors rated 100 hp or larger, their terminations shall be not less than 1.2 m from any part of the motor.