Agreed, but the code is the bare MINIMUM requirements.It just seems silly to make them GFCI since you need a ladder to hang the lights...
True, but anyone can touch the aluminum downspout that is attached to the eavestrough that I run over with the lawnmower. :thumbsup:So somebody shouldn't be able to touch them by hand...
I forgot about the 2.5m rule; I guess it's never applied for anything I've installed. I think if I was installing it I would put a GFCI on it anyway just to be safe.Maybe this:
Receptacles for residential occupancies 26-710 General
except for automobile heater receptacles provided in conformance with Rule 8-400, all receptacles installed outdoors and within 2.5 m of finished grade shall be protected with a ground fault circuit interrupter of the Class A type;
^^ :no:I was wondering if the re-work brackets (F-clips is what my J-man calls them) would work on the tin?
You don't want the GFCI up in the soffit though; makes it hard to reset. Feed it from a GFCI receptacle at ground level or with a GFCI breaker.I forgot about the 2.5m rule; I guess it's never applied for anything I've installed. I think if I was installing it I would put a GFCI on it anyway just to be safe.