Originally Posted by brian john
The current seeks the source, it is being supplied from.
Speaking of 3 phase 4 wire or single phase 3 wire, there are two types of ATS a 3/2* pole only the phase conductors transfer and a 4/3* pole the phase and neutral conductors transfer. With a 3 pole ATS the neutral conductor in the generator MUST NOT BE BONDED TO GROUND. In a 4 pole ATS the neutral is bonded to ground as a 4 pole ATS is a SDS separately derived system.
* 3/2 3 pole 3 phase 4 wire, 2 pole single phase 3 wire
* 4/3 4 pole 3 phase 4 wire, 3 pole single phase 3 wire
So, does this mean if the neutral is not switched in a transfer switch it s not considered a seperately derived system? We live on the north coast and had lots of damage to homes due to the recent storm,and are installing lots of transfer switches,and repairing lots of meters taken down by trees. Today we installed a dpdt 200a switch. we ran from the meter to the dpdt with 3 wire se cable, ran from the dpdt to main breaker panel with 4 wire ser, then from portable generator to dpdt switch. The journeyman seemed to have problems with how the super was telling him to ground the dpdt switch. First, the neutral is not switched only the phase conductors, the neutral from the meter and going to the mb panel are tied together with the grounding electrode conductors in the 200a dpdt switch, also we seperated all the grounds and neutrals in the mb panel because it was not the first point of disconnect anymore. One of the first things my boss told me when i started was remember to tie all grounds and neutral plus electrodes together at first point of disconnect, but Im thinking that may not apply here. Any info will be greatly appreciated.

The current seeks the source, it is being supplied from.
Speaking of 3 phase 4 wire or single phase 3 wire, there are two types of ATS a 3/2* pole only the phase conductors transfer and a 4/3* pole the phase and neutral conductors transfer. With a 3 pole ATS the neutral conductor in the generator MUST NOT BE BONDED TO GROUND. In a 4 pole ATS the neutral is bonded to ground as a 4 pole ATS is a SDS separately derived system.
* 3/2 3 pole 3 phase 4 wire, 2 pole single phase 3 wire
* 4/3 4 pole 3 phase 4 wire, 3 pole single phase 3 wire
So, does this mean if the neutral is not switched in a transfer switch it s not considered a seperately derived system? We live on the north coast and had lots of damage to homes due to the recent storm,and are installing lots of transfer switches,and repairing lots of meters taken down by trees. Today we installed a dpdt 200a switch. we ran from the meter to the dpdt with 3 wire se cable, ran from the dpdt to main breaker panel with 4 wire ser, then from portable generator to dpdt switch. The journeyman seemed to have problems with how the super was telling him to ground the dpdt switch. First, the neutral is not switched only the phase conductors, the neutral from the meter and going to the mb panel are tied together with the grounding electrode conductors in the 200a dpdt switch, also we seperated all the grounds and neutrals in the mb panel because it was not the first point of disconnect anymore. One of the first things my boss told me when i started was remember to tie all grounds and neutral plus electrodes together at first point of disconnect, but Im thinking that may not apply here. Any info will be greatly appreciated.