I got a call last night from a long time customer, he has a site where the electrician wanted to saw cut a trench for a 2" conduit, he said no to them. They have come back and want to saw cut a glad width to install a comm cable.

Would this be legal, a comm cable inserted in a saw width cut that is flash patched.


And before you answer

Yes I can look it up, BUT I AM LAZY.
No I do not do communication were so I do not know the answer off the top of my head.
No I am not a code expert so I do not know the answer off the top of my head.

What non-answers am I missing
 

·
Registered
Joined
·
8,050 Posts
Use direct burial rated cable and I don't see why not. When it comes to comm cable I use the code voice inside my brain
 

·
Coffee drinking member
I pretwist and then use wire nuts. Solder pots rule.
Joined
·
13,986 Posts
ponyboy said:
Use direct burial rated cable and I don't see why not. When it comes to comm cable I use the code voice inside my brain
But is it buried or incapsulated in concrete?
 

·
Banned
Joined
·
15,674 Posts
The first thing to do would be to find a communication cable that would be approved for being encased in concrete. Not sure if they make a communication cable for that application?
 

·
Retired Account
Joined
·
39,697 Posts
Maybe 830.47 & table 830.47 Brian ....(we're lousy with comm crews trying to bring Vt into the 20th century....:rolleyes:) ~CS~
 