Discussion Starter · #1 ·
Is everything in a commercial kitchen presumed to run at once? Pretty sure it all falls under continuous draw. At 125% I'm at 240A with a 200A service. If the load calculation requires enough for everything running at once, I'm going to have bad news for my customer.
 

·
Registered
Joined
·
14,448 Posts
220.56 Kitchen Equipment — Other Than Dwelling Unit(s).



It shall be permissible to calculate the load for commercial electric cooking equipment, dishwasher booster heaters, water heaters, and other kitchen equipment in accordance with Table 220.56. These demand factors shall be applied to all equipment that has either thermostatic control or intermittent use as kitchen equipment. These demand factors shall not apply to space-heating, ventilating, or air-conditioning equipment.
However, in no case shall the feeder or service calculated load be less than the sum of the largest two kitchen equipment loads.

Table 220.56 Demand Factors for Kitchen Equipment — Other Than Dwelling Unit(s)
Number of Units of EquipmentDemand Factor
(%)
1100
2100
390
480
570
6 and over65
 

·
Registered
Joined
·
216 Posts
Discussion Starter · #4 ·
220.56 Kitchen Equipment — Other Than Dwelling Unit(s).



It shall be permissible to calculate the load for commercial electric cooking equipment, dishwasher booster heaters, water heaters, and other kitchen equipment in accordance with Table 220.56. These demand factors shall be applied to all equipment that has either thermostatic control or intermittent use as kitchen equipment. These demand factors shall not apply to space-heating, ventilating, or air-conditioning equipment.
However, in no case shall the feeder or service calculated load be less than the sum of the largest two kitchen equipment loads.

Table 220.56 Demand Factors for Kitchen Equipment — Other Than Dwelling Unit(s)
Number of Units of EquipmentDemand Factor
(%)
1100
2100
390
480
570
6 and over65
Yes, I went to the truck and grabbed the book. Customer did say everything will pretty much be running. I didn't even include the HVAC units. I suppose the dishwasher might be intermittent. He has some basic 120v plug in coolers I didn't even count.

Suppose I use 65% as per 220.56. Is that the final figure or do I need 125% of that? I'm afraid this is going to be a squeaker.
 

·
Administrator
Retired EC
Joined
·
24,324 Posts
Is the service 3 phase 208V and did you calculated the load based on 3phase.. IOW, divide the kw by 360V
 
  • Like
Reactions: taglicious

·
Registered
Residential, lite comm., Industrial
Joined
·
2,944 Posts
That doesn’t create confidence. Why not phone the inspection department first?
Much better idea
do you want this job?
if so you need to present to the customer as though you are on top of it
and then do what you have to , to actually be on top of it
this way you can advise him from an informed position and be right about what will and will not work
that way he can make the decision to continue or quit
avoid liability, whether advice or actual install
 

·
Registered
Joined
·
216 Posts
Discussion Starter · #11 ·
Is the service 3 phase 208V and did you calculated the load based on 3phase.. IOW, divide the kw by 360V
No, it's 240V. I want off the amperage rating on the equipment plates. Came to 192A for just the equipment. Not included HVAC, general plugs (which will run smaller equipment) or lighting. Just told him he will need a new feed and panel. Hopefully not a new meter socket.
Much better idea
do you want this job?
if so you need to present to the customer as though you are on top of it
and then do what you have to , to actually be on top of it
this way you can advise him from an informed position and be right about what will and will not work
that way he can make the decision to continue or quit
avoid liability, whether advice or actual install
Agreed. I told him he will need to bring in another set of feeders for an additional panel. After thinking about all the stuff I didn't include, I don't think the dog he has is going to hunt.
 

·
Registered
Joined
·
216 Posts
Discussion Starter · #14 ·
Poco wants me to jump through hoops just to find out what meter socket I need. Looks like it will be a CT cabinet. I don't think the customer wants to pay to have it done right. He'll get someone to Jerry rig it and then they will all end up in Court. Good luck with that guys.
 

·
Registered
Residential, lite comm., Industrial
Joined
·
2,944 Posts
Poco wants me to jump through hoops just to find out what meter socket I need. Looks like it will be a CT cabinet. I don't think the customer wants to pay to have it done right. He'll get someone to Jerry rig it and then they will all end up in Court. Good luck with that guys.

time to back out and move on
 