Discussion Starter · #1 ·
Two Q's
1. For EV charger loads only, does the panelboard need to be sized for the sum of the continuous duty loads (i.e. number of chargers x charger amps) or the sum of the OCPD for those EV chargers?
2. For EV charger loads only, if a performance meter socket is used to measure consumption, must it be sized for the sum of the continuous duty loads (i.e. number of chargers x charger amps) or the sum of the OCPD for those EV chargers?
 