I replaced 10 2X2 Fluorescent troffers with LED troffers. The LED troffers flicker while the compressor is running.
Details:
1. Flickering occurs during the entire time the compressor is running which may be a duration of 10 minutes.
2. I measured voltage drop at a fixture when the compressor was off and again while it was on. On: 119V. Off 115V
3. Spec on LED troffers says 110V -277V
4. Connected a Variac to one LED fixture and dialed down to 100V. No flicker
5. Customer said flurorescents used to flicker. There was a combination of magnetic and electronic and I'm not sure which were or were not flickering.
6. New LED troffers have 0-10V dimming but this feature is not connected.
7. Compressor and lighting circuit both come from a 208V 3-phase panel. The compressor takes 2 of these legs with a dedicated circuit. The lights share a leg - not a circuit - with the compressor. The lights are on a dedicated circuit.