conduit body support NEC 314.23 (E) exception

11K views 2 replies 3 participants last post by  MDShunk 
Does anyone know if you can support a conduit "T" with only one support?
You can, but the exception allows rigid metal conduit to support a conduit body without any additional support for the conduit body. The conduit should be supported in accordance with 344.30 for RMC.

Chris
 