What I had:
3 big machines that take a 100A, 3 phase 480v Circuit each.
Already had bought about 1000' of #2 to take care of these.
I had intended running seperate conduits for each. Well, it turned out there was an existing and empty 2 1/2" EMT comming from the I line running really close to where I need to get my circuits. So plans started changing. Checked the fill for the 2 1/2" and #2 and found I could put 20 #2s in that 2 1/2"!
I only needed to put 9 wires through it with a ground, so I thought it'd be all good. Welllll, I got to thinking I'd heard about this derating thing. So I started checking into it in the code book and found Table 310.15(B)(2)(a).
For 7-9 wires it says to make it 70 percent of the rated value. The rated value of 3 #2's in a raceway is 130A based on ambient temps. So having 9 #2's would take it down to 91A, correct? (Which I could have easily upsized the wire, or made it a tap to my Junction box comming off of a 300-350A breaker, but I already had the wire on the jobsite).
Now, what I've been wondering most is, does it matter what size conduit is used when figuring derating values? I mean, if I would have pulled the 9 hots and 1 ground I would have only taken up about half of the rated conduit fill for the 2 1/2". Which means there is more air space in that 2 1/2" than a 2".
I didn't figure in for voltage drop because I've always heard it's really unnoticable until you get over 100 feet or so, and this was only around 70-80 feet.
Also, how much emphasis do you guys put behind the ambient temperature adjustment? And why is there the adjustment? Is it because the insulation can get that hot in addition to the heat of the resistance of the wire inside?
I'm sorry this is so long, but this is the biggest job I've been in charge of on my own and I'm learning alot of new things on this job. I want to be in the right with things I do. I ended up only running two of those circuits into a 2x2 jbox through the 2 1/2" which derated it to only 104. I'm running another seperate conduit for the other one. I asked another electrician that works with us his opinion on it and he told me, "I ain't ever derated no wire". He's been doing electrical work way longer than I have. I've only been at it for around 6 years or so.
Thank you all in advance for any insight.
3 big machines that take a 100A, 3 phase 480v Circuit each.
Already had bought about 1000' of #2 to take care of these.
I had intended running seperate conduits for each. Well, it turned out there was an existing and empty 2 1/2" EMT comming from the I line running really close to where I need to get my circuits. So plans started changing. Checked the fill for the 2 1/2" and #2 and found I could put 20 #2s in that 2 1/2"!
I only needed to put 9 wires through it with a ground, so I thought it'd be all good. Welllll, I got to thinking I'd heard about this derating thing. So I started checking into it in the code book and found Table 310.15(B)(2)(a).
For 7-9 wires it says to make it 70 percent of the rated value. The rated value of 3 #2's in a raceway is 130A based on ambient temps. So having 9 #2's would take it down to 91A, correct? (Which I could have easily upsized the wire, or made it a tap to my Junction box comming off of a 300-350A breaker, but I already had the wire on the jobsite).
Now, what I've been wondering most is, does it matter what size conduit is used when figuring derating values? I mean, if I would have pulled the 9 hots and 1 ground I would have only taken up about half of the rated conduit fill for the 2 1/2". Which means there is more air space in that 2 1/2" than a 2".
I didn't figure in for voltage drop because I've always heard it's really unnoticable until you get over 100 feet or so, and this was only around 70-80 feet.
Also, how much emphasis do you guys put behind the ambient temperature adjustment? And why is there the adjustment? Is it because the insulation can get that hot in addition to the heat of the resistance of the wire inside?
I'm sorry this is so long, but this is the biggest job I've been in charge of on my own and I'm learning alot of new things on this job. I want to be in the right with things I do. I ended up only running two of those circuits into a 2x2 jbox through the 2 1/2" which derated it to only 104. I'm running another seperate conduit for the other one. I asked another electrician that works with us his opinion on it and he told me, "I ain't ever derated no wire". He's been doing electrical work way longer than I have. I've only been at it for around 6 years or so.
Thank you all in advance for any insight.