We are currently commissioning a conveyor system.
the system has about 20 fractional horsepower motors at 600v.
the first conveyor is the shortest, and so far, has several days worth of run time on site, and several days of run time at the shop.
This morning, the VFD faulted, overload. the motor was running at double the name plate amps. There was no obvious mechanical problem with the conveyor.
motor was isolated from the gearbox and still drew twice fla
motor was wired to a different VFD and still drew twice fla
a known good motor was wired to original VFD that had the bad motor and it ran at nameplate fla no problem
New spare motor was brought in from the shop. It was installed, turned on and within seconds it was up at double nameplate amps, exactly the same as the first. Isolated from gearbox, run on a different vfd, same result.
both motors fla were 0.8 amps and both motors drew 1.8amps
pulled the motors and isolated the wiring. Meggered out the windings and they were fine, but 1 set of windings on both motors (the same winding on both) was showing half the resistance as the other two windings. 20ohms vs 40 for the other two.
I have 2 more motors coming in tomorrow
interestingly, the motors were within 20 digits on their serial numbers.
I am going to bring the megger to site and check the cable, which is about 100 feet of 14/4 + aux VFD tray cable run in a enclosed wire mesh cable tray
but i dont see how the cable could be damaged and allow the motor to run
motor was not single phasing
any thoughts/suggestions?
the system has about 20 fractional horsepower motors at 600v.
the first conveyor is the shortest, and so far, has several days worth of run time on site, and several days of run time at the shop.
This morning, the VFD faulted, overload. the motor was running at double the name plate amps. There was no obvious mechanical problem with the conveyor.
motor was isolated from the gearbox and still drew twice fla
motor was wired to a different VFD and still drew twice fla
a known good motor was wired to original VFD that had the bad motor and it ran at nameplate fla no problem
New spare motor was brought in from the shop. It was installed, turned on and within seconds it was up at double nameplate amps, exactly the same as the first. Isolated from gearbox, run on a different vfd, same result.
both motors fla were 0.8 amps and both motors drew 1.8amps
pulled the motors and isolated the wiring. Meggered out the windings and they were fine, but 1 set of windings on both motors (the same winding on both) was showing half the resistance as the other two windings. 20ohms vs 40 for the other two.
I have 2 more motors coming in tomorrow
interestingly, the motors were within 20 digits on their serial numbers.
I am going to bring the megger to site and check the cable, which is about 100 feet of 14/4 + aux VFD tray cable run in a enclosed wire mesh cable tray
but i dont see how the cable could be damaged and allow the motor to run
motor was not single phasing
any thoughts/suggestions?