How is the lug attached to the panel?
Electricity will take every path to ground but it will also use the least resistant path for a greater portion of the load. A ground rod would have so much resistance that virtually no current will travel there.Thanks a lot, Dennis! I guess I will be leaving it as is. The customer was also asking me this, and for the life of me, I do not know the answer to this question - why does the electricity prefer to keep on going through the neutral wire rather than choosing their insulated ground wire that runs to the ground rod to find its path to the ground, since ground and neutral are connected at the bus bar? I just know this is the way it is done, but it certainly is very peculiar. Thanks for your help.
This post will be short lived. Are you an apprentice?Thanks a lot, Dennis! I guess I will be leaving it as is. The customer was also asking me this, and for the life of me, I do not know the answer to this question - why does the electricity prefer to keep on going through the neutral wire rather than choosing their insulated ground wire that runs to the ground rod to find its path to the ground, since ground and neutral are connected at the bus bar? I just know this is the way it is done, but it certainly is very peculiar. Thanks for your help.
Go to his link and you can enlarge the picture and read it better. I said better, not perfect.With that kind of organized note labeling on you photo (which by the way Sunny Boy, us near deads are unable to actually read....) you show me that you are going to probably get along really well in the trade. Thats the stuff right there. Be like that in all your work, organized and very detailed.
That and if this is a service disconnecting means then that bonding jumper needs to go into that hole on the busbar on the left side of the box...ARTICLE 352— RIGID POLYVINYL CHLORIDE CONDUIT: TYPE PVC
352.46 Bushings. Where a conduit enters a box, fitting, or
other enclosure, a bushing or adapter shall be provided to
protect the wire from abrasion unless the box, fitting, or
enclosure design provides equivalent protection.
John .,If that is a service extension, why the breaker or disconnect? Would the addition of a breaker make it a feeder requiring four conductors? I am asking.
If the HO had used double lug adapters he should have just left the meter enclosure and landed the 3 service conductors into another service panel (shed) with main breaker. But the addition of the breaker should make this a 4 wire feeder? I am asking.