Who derates? Barely any contractor ever debates, never done it in the last 12 Years of my career.
Professionals who care about doing things up to code and not cutting corners that an inspector may or may not see. If we can't take the code seriously how can we be expected to be taken seriously.Who derates? Barely any contractor ever debates, never done it in the last 12 Years of my career.
Edit: I see you said just over 24 inches. Cut the conduit shorter.310.15(b)(3)(a)(2) derating due to conductor fill only applies to conduits longer than 24 inches.
You are also nit derating correctly. If you had to derate in this case you would see there are 32 current carrying conductors. Whitch leads you to 40% derate. So for instance you had a 20 amp rated circuit. Your math would be 20/.40=50 your conductor must be rated at 50 amps. A number 8 at 90 degrees is rated at 55 amps so it would be acceptable.
I would derate a little differently than you suggest. Without pulling out a codebook, and using your 40% as the factor, #10 THHN is rated at 40 amps at 90c. 40% of 40 amps is 16 amps. You can use the next size breaker up, 20 amps, as long as you don't exceed 800 amps. You can use the actual temperature rating of the conductor (90c) to start derating from and as long as you don't exceed the lower temperature rating when sizing the breaker.:thumbsup:310.15(b)(3)(a)(2) You are also not derating correctly.
Only if the load is less than 16 amps could you use next size up rule.I would derate a little differently than you suggest. Without pulling out a codebook, and using your 40% as the factor, #10 THHN is rated at 40 amps at 90c. 40% of 40 amps is 16 amps. You can use the next size breaker up, 20 amps, as long as you don't exceed 800 amps. You can use the actual temperature rating of the conductor (90c) to start derating from and as long as you don't exceed the lower temperature rating when sizing the breaker.:thumbsup:
Any thoughts, or have I been doing it wrong all along?![]()
Keep reading the same article you will see it does not apply to rec circuits for cord and plug equip. Rules out most residential applications.I would derate a little differently than you suggest. Without pulling out a codebook, and using your 40% as the factor, #10 THHN is rated at 40 amps at 90c. 40% of 40 amps is 16 amps. You can use the next size breaker up, 20 amps, as long as you don't exceed 800 amps. You can use the actual temperature rating of the conductor (90c) to start derating from and as long as you don't exceed the lower temperature rating when sizing the breaker.:thumbsup:
Any thoughts, or have I been doing it wrong all along?![]()
Thanks, must have hi-litghted that section in my code book with the black magic marker.Keep reading the same article you will see it does not apply to rec circuits for cord and plug equip. Rules out most residential applications.
Hi All,
... These circuits will be traveling through conduit for just over 24 inches and I am thinking I will have to de-rate each of the conductors per table 310.15(B)(2)(a) [2008 NEC].... . If my thinking is correct, I will have to de-rate each of these wires to about 40 percent of their allowable ampacity per table 310.16. That will mean I will have to run a number 6 for each 20A circuit. Is that right?....Whoa! .
Freaking brilliant.Put a Jct. Box In the pipe run that is Over 24 inches .
Then you have 2 nipples , each under 24 inches .
Pete