Reading voltages to ground do nothing but confuse people. However, you did realize the secondary was not grounded, which it should be. The XFMR needs to be grounded too.
What advantage does a delta to delta XFMR provide? Delta to wye is the way to go. Especially in an industrial environment. Many electronic devises such as AC drives do not operate well on delta derived sytems. Plus you get a true neutral.
What advantage does a delta to delta XFMR provide? Delta to wye is the way to go. Especially in an industrial environment. Many electronic devises such as AC drives do not operate well on delta derived sytems. Plus you get a true neutral.