Delta-delta Transformer Voltage Problems

34593 Views 3 Replies 4 Participants Last post by  John Valdes
I Have A Three Phase Delta-delta 480vac To 240vac Transformer. This Transformers Has Me Concerned Due To The Voltage Readings To Ground. This Transformer Feeds A 3 Wire 240vac Panel.

When We Read Phase To Phase It Reads 240vac. I Measured Phase A To Ground And Read 10vac. Phase B To Ground Was 240vac, And Phase C To Ground Was 240vac. Phase A Increased To 120vac While Phase C Decreased To 120vac. We Used Two Meters And Witnessed Simultaneous Voltage Change On Those Two Phases.

These Connect Numerous Loads Which Do Not Seem To Be Effected By The Voltage Fluctuating. Once In Awhile The Machines Blows An Incoming Fuse, But Does Not Trip The Breaker.

I Know That This Is An Ungrounded Delta-delta Transformer. Do I Need To Ground One Phase Of The Secondary? Is It Possible That The Transformer Is Breaking Down?

P.s. We Are Only Using Single Phase 240vac Loads And Three Phase 240vac From This Panel I Mentioned Above.:(

Thanks For Suggestions
1 - 1 of 4 Posts
The reason you're getting odd voltages is because the xfmr secondary is not grounded, and thus there's no reference point. You're reading meter impedance, VERY high impedance ground faults (not to worry, they're so small there's no hazard), capacitance in the test leads, etc.

Does this xfmr have an X0 or X4 terminal? If so, it's the mid-point of one of the phases, and if you're going to ground it, that's the spot. Then you'll have a 240/120 3PH 4W delta system. There are thousands of these in operation. You'll read 120V to ground on 2 phases, 208 to ground on the 3rd, and 240 between any two phases.

If the xfmr has just X1, X2, and X3, then you'll need to study the system a bit more to determine if it should be grounded. If it is to be grounded, ground X2, and you'll have a grounded B system. Also known as a corner grounded system. There are not a huge number of these still in use, they were more popular years ago. Be careful using the grounded B with single phase loads as at least one of the legs will be 240V to ground. Usually it's ok, but this is one thing that needs to be studied.

I've seen many of these systems ungrounded, and other than a possible code violation, very few problems. I'd actually suggest that 'if it ain't broke, don't fix it'.
See less See more