The primary low side is protected by the feeder breaker and is most likely fed from a grounded system already.
The secondary high side you want to protect should have one phase grounded. This will give you 600V-to-ground on the remaining two phases. And you'll have what's called a corner-grounded delta.
You need to be careful about how you treat your grounded phase. I don't have the Good Book in front of me, but for one thing, you can't use fuses in your secondary overcurrent protection because your grounded-phase overcurrent protection needs to open all the remaining phases.