Electrician Talk banner

1 - 5 of 5 Posts

·
Registered
Joined
·
1 Posts
Discussion Starter #1
I am looking at wiring a Delta to delta step up transformer. 30 KVA. 208 3 phase primary and 600 3 phase secondary. My question is how do you safely groung the transformer so that if you have a phase go to ground it will trip the three phase breaker on the primary side.
 

·
Donuts > Fried Eggs
Joined
·
17,054 Posts
The primary low side is protected by the feeder breaker and is most likely fed from a grounded system already.

The secondary high side you want to protect should have one phase grounded. This will give you 600V-to-ground on the remaining two phases. And you'll have what's called a corner-grounded delta.

You need to be careful about how you treat your grounded phase. I don't have the Good Book in front of me, but for one thing, you can't use fuses in your secondary overcurrent protection because your grounded-phase overcurrent protection needs to open all the remaining phases.
 
1 - 5 of 5 Posts