I have two 120 volt loads for a carwash vacuum system. Each vacuum pulls 24 amps.
so I will have 4 ccc’s feeding this system. Ambient temp is controlled.
Thhn wire, derated at 80% = 32 amps. Can I still use #10 wire with a 30 amp breaker?
Thanks
 

·
Registered
Joined
·
13,403 Posts
I have two 120 volt loads for a carwash vacuum system. Each vacuum pulls 24 amps.
so I will have 4 ccc’s feeding this system. Ambient temp is controlled.
Thhn wire, derated at 80% = 32 amps. Can I still use #10 wire with a 30 amp breaker?
Thanks
Two pole breaker and MWBC gets three current carrying conductors.
 

·
Registered
36th year apprentice & Floor Sweeper
Joined
·
1,737 Posts
Yes.
 