IF you have say 90 C and 60 C rated wires in the same conduit in an area with an ambiet air temperature of 40C, how do you derate them for temperature?
IGNORING THE EQUIPMENT TEMPERATURE RATING
4-004 says you have to take the curreent rating from Table 2 using the lowest temperature rated wire, so these amapcitied from this case would come from the 60C column.
The correction factor for the 40C ambient comes from Table 5A. Heres the question, do you derate BOTH conductors using the 60C column or do you take the derating for the 90C using the derating factor from the 90C column and the 60C wire with the derating factor from the 60C column.
In a nut shell do you derate the 90C wires TWICE?
IGNORING THE EQUIPMENT TEMPERATURE RATING
4-004 says you have to take the curreent rating from Table 2 using the lowest temperature rated wire, so these amapcitied from this case would come from the 60C column.
The correction factor for the 40C ambient comes from Table 5A. Heres the question, do you derate BOTH conductors using the 60C column or do you take the derating for the 90C using the derating factor from the 90C column and the 60C wire with the derating factor from the 60C column.
In a nut shell do you derate the 90C wires TWICE?