Can anyone help me figure out where they get the 1va x 600 sq.ft. in this example?
The only places with 1va are armories and auditoriums, churches and then assembly halls..Table 220.12?
Maybe there?220.14
K) Banks and Office Buildings. In banks or office build- ings, the receptacle loads shall be calculated to be the larger of (1) or (2):
(1) The calculated load from 220.14(I)
(2) 11 volt-amperes/m2 or 1 volt-ampere/ft2
What the hell, a Canadian quoting NEC rules?Table 220.12?
I couldn't figure out that CEC, it's too complicated!What the hell, a Canadian quoting NEC rules?
Can anyone help me figure out where they get the 1va x 600 sq.ft. in this example?