receptacles in a room must be no more than 3.6m apart. 1.8m from any point in the room must be accessible to a receptacle.
26-712
Receptacles for dwelling units (see Appendices B and G)
This Rule applies to receptacles for dwelling units (including single dwellings) as follows:
(a) except as otherwise provided for in this Code, in dwelling units duplex receptacles shall be installed in the finished walls of every room or area, other than kitchens, bathrooms, hallways, laundry rooms, water closet rooms, utility rooms, or closets, so that no point along the floor line of any usable wall space is more than 1.8 m horizontally from a receptacle in that or an adjoining space, such distance being measured along the floor line of the wall spaces involved;
26-712
Receptacles for dwelling units (see Appendices B and G)
This Rule applies to receptacles for dwelling units (including single dwellings) as follows:
(a) except as otherwise provided for in this Code, in dwelling units duplex receptacles shall be installed in the finished walls of every room or area, other than kitchens, bathrooms, hallways, laundry rooms, water closet rooms, utility rooms, or closets, so that no point along the floor line of any usable wall space is more than 1.8 m horizontally from a receptacle in that or an adjoining space, such distance being measured along the floor line of the wall spaces involved;