Inspectors will often mark something like "No GFCI near sink", but the outlets are in fact protected because they are downstream from a GFCI someone else. Is this still code compliant. Or does every outlet within 6 feet of the sink or an outdoor location need to be a GFCI outlet now.
 

·
Mad as Hell Member
Joined
·
2,936 Posts
Up here it needs to be GFCI protected, regardless if it's protected by a breaker at the panel or a GFCI receptacle in another room.
 

·
Registered
Joined
·
385 Posts
Inspectors will often mark something like "No GFCI near sink", but the outlets are in fact protected because they are downstream from a GFCI someone else. Is this still code compliant. Or does every outlet within 6 feet of the sink or an outdoor location need to be a GFCI outlet now.
Don't do resi often but it's not a code I'm aware of. Tell the inspectors they need to get a plug tester. That's what they use here.
 

·
I own stock in FotoMat!
Joined
·
39,118 Posts
Tell the inspectors to read the Code.

The 6-foot-from-sink rule disappeared in 1996.
 