Can anyone report any experiences they've had doing this?

I understand the basic concept-
1) Sine Filter on the Output of the Drive
2) Run the Drive in V/Hz
3) Output of the drive goes to a 480/4160v step up transformer
4) Profit?

Most of the drives reps will not give any info on this, and go on about how it's not recommended etc.

I hate to say it but in this case I'm inclined to think a lot of the negative comments are because it's in the best interests of the drives rep to sell you a much more expensive drive that you by and large also cannot service yourself. Also much of the time we have limited space in the electrical room and and MV drive won't fit. An LV drive will, and the step up transformer could be mounted outside somewhere.

Anyways just wonder if anyone has any thoughts or experiences to share, especially regarding any special requirements with respect to the transformer.
 

·
Donuts > Fried Eggs
Joined
·
17,042 Posts
It might be awesome, because the transformer would act like a big load-reactor and automatically attenuate a lot of the transients and carrier-frequency noise.

It might be terrible, because the transformer would act like a big-load reactor and attenuate the fundamental frequency you were using to drive the motor.

The biggest concern I would actually have would not be to the drive itself, but for the transformer that is optimized to run at 60Hz. You start running a much lower frequency through it, and you're reducing the impedance, and increasing your current, possibly disasterously.

I honestly don't know, except to say I've never seen or heard of this type of install. Jraef will be along shortly to explain whether it's a good idea. :laughing:
 

·
Registered
Joined
·
438 Posts
Discussion Starter · #4 ·
Obviously it's an engineered solution and that work will be done in any case.
The best engineering also pays attention to whatever field references might be available. Hence the question.

I design and start up lots lv drive systems in the 450-700hp range, I'm comfortable with them and have lots of proven designs I can re-use and tweak for most applications. If I can leverage this for MV systems I will. It certainly is done.
 

·
Registered
Joined
·
1,948 Posts
Obviously it's an engineered solution and that work will be done in any case.
The best engineering also pays attention to whatever field references might be available. Hence the question.

I design and start up lots lv drive systems in the 450-700hp range, I'm comfortable with them and have lots of proven designs I can re-use and tweak for most applications. If I can leverage this for MV systems I will. It certainly is done.
I remember reading an article about an engineer researching this, but it's been several years and can't remember where I read it at. I'm out of my scope on this, as I'm really nothing more than parts changer. I'm guessing if anybody on this site would be familiar with this, it would be JRaef.
 

·
Registered
Joined
·
14,460 Posts
Not a good idea with a standard xformer. It won't like the changing frequency and harmonics of the PWM drive output, it'll overheat.

You can get custom drive output step up xformers. They are common for ESP installs, although now MV drives are becoming more cost effective.
 

·
Registered
Joined
·
438 Posts
Discussion Starter · #7 · (Edited)
I believe that's a major reason for going beyond a load reactor or dv/dt output filter and using a full-on sine filter- the sine filter gets spec'd to give an IEEE compliant waveform on the secondary. (Or, I guess the intent is that it reduces harmonic content to levels that are inside the design limits of the transformer, anyway).

That being said you have a point though in that maybe it's cheaper and simpler to get a "fancy" transformer that can handle the dv/dt etc, less parts to mount, terminate to, keep cool, etc. that would be really good. I guess that's a big part if my question that I wasn't very clear on- I'm wondering just what sort of products are out there.

I've heard the name ESP come up in other conversations as well so thanks for mentioning them. I will probably try to talk to them next week.
 

·
Registered
Joined
·
782 Posts
just a quick quick question has anyone used the mv drives on transformers?
is it practical?
apart from the reduction in harmonics are there any more advantages
 

·
Registered
Joined
·
5,513 Posts
ESP is an acronym for Electrical Submersible Pump (probably because it sounds better than "down hole pump" when speaking in mixed company). He's right, the XFMR -VFD -XFMR method was very common for that industry, mainly for two reasons:

1) The applications were always pumps, which means they did not need Sensorless Vector Control. One downside of doing it this way is that the VFD cannot use a motor model that remains accurate because of the added impedance of the transformer, which changes dynamically with frequency. The motor does too, it's just that the doubly dynamic interactions are too complex for SVC drives to track. But for the most part, you don't need SVC on a centrifugal load like a pump, so having to put the VFD in V/Hz mode is no big deal.

2) The ESPs were sold as an engineered packaged solution, so the step-up transformer design issues were dealt with by the vendors, who were looking for a cheaper solution than MV drives. And yes, there are several concerns for the transformers used. The ESP vendors initially went with the transformer mfrs who suggested specially built core designs to deal with the issues of operating with variable frequencies and high harmonics. But as more vendors got into it and pricing pressures increased, some of the low end ESP vendors started using off-the-shelf transformers, knowing they would likely outlive the warranty anyway, but leaving the future mess to the end users. But for a long time, MV drives were only available from a few vendors, so the ESP packagers could not negotiate pricing as easily as they liked. That's no longer the case, so the ESP vendors are tending to move away from that practice.

The argument the ESP pump packagers used to allow it to appear less expensive however was that the load side transformer was not a transformer, it was a part of the motor circuit. Therefore, it was being protected BY the same motor protection inherent in the VFD and needed nothing else. Not all inspectors agree with that however, and if you have to add primary and/or secondary (MV) protection and disconnects to that load side transformer, it immediately becomes economically unviable. If you use fuses for the protection, you also introduce the possibility of only one of the fuses opening on the load side of the VFD, not something the VFD mfrs. are thrilled about. In fact, they are not thrilled about opening a CB on the load side either, but it's at least acceptable in an emergency.

Probably the most overlooked issue is however, that there are added losses in that secondary transformer which are now permanent in the motor circuit, and the loss percentages increase as speed decreases (although net kW losses decrease because load decreases). It just means that the energy that you can save at reduced flow is less than if you went directly from a MV drive to the motor. Since this is typically only done on large motors, the $$$ add up quickly. The counter argument is that if you have a load reactor on the output side, it's the same as having a transformer. But that's not really true, because the reactor is simply magnetic, so the losses through it are very low. A transformer has added winding ratios, so the I^2R losses are added to the equation as well. You have all that extra winding wire now on the low voltage side added to the theoretical circuit length.

The issue of MV drives only being able to be serviced by MV technicians has also gone away for the most part. It was a problem initially, but several of the major players redesigned the drives years ago in such a way as to allow anyone to service them now. Some states require MV termination certification, but that will be the case no matter what, because if you have a MV motor, you will have to terminate MV cables somewhere.
 

·
Registered
Joined
·
782 Posts
that answers it jraef thanks.vfds have not been in my country for along time and that mv application was new to me.but working in a company where almost all machines use plc and vfds has given me a chance to program many both AC and DC from different. manufacturers
thanks for the info
 