The motor is a 120/240V, 19.5/9.5A table saw in a commercial wood shop. Is there any reason to convert the current 120V setup to 240V? Watts=watts, but what about efficiency, longevity, strength under load, etc?
Why? The current though the windings should be the same no matter what voltage you are using, and if the current is the same than the I²R losses are too.... A lower voltage motor tends to run warmer than a higher voltage motor of same HP and RPM.
...
The motors torque doesn't ever change. Who cares what voltage it is. The motors rated for a set duty. If you wire that motor with the correct conductors the demand for electrons will always be their.This makes absolutely no sense whatsoever, but if the motor is connected for 240, it will have more pull-up and breakdown torque.
In other words, the guys who use it will very likely notice more power.
Even if the wire for 240 is smaller, there's still a noticeable difference.
Yes, I realize this violated the laws of physics, but the actual fact is.......
So yes; I would absolutely connect it for 240.
In theory, yes. In actual reality, no; it'll have more torque all the way around when connected for the higher voltage. Ask any old-time carpenter if his saw runs better on '110' or '220' and every one of them will say the same thing. 220.The motors torque doesn't ever change. Who cares what voltage it is. The motors rated for a set duty. If you wire that motor with the correct conductors the demand for electrons will always be their.
And there is is...If I'm not mistaken it should also draw a lower inrush current spike at startup when wired for 240v.
I picked that avatar because it's a half way real representation of what I look like, although I have a beard.Does anyone else watch Family Guy and expect to learn something new every time you see Peter?
GREAT Post! Thanks! :thumbup:19.5A, people will likely run #10 and call it good, and the NEC says that's acceptable. But that motor will pull upward of 117A at startup. If you use 230V at 9.5 A, the starting current only gets to 57A.
Yes, 600% is the safe bet. A few motors will pull more, many will be less, but 600 is a good place to land and be safe in your assumptions.GREAT Post! Thanks! :thumbup:
How did you arrive at this inrush current? Roughly 6x the continuous load?