I am giving an estimate on a new over head service to feed a duplex building. I want to use 1 service drop and then feed 2 meters, with a load center for each. They will be next to each other on the same wall. Should I install a gutter above the 2 meter main panels and splice the feed with polaris taps? Is there a better way to do this?
 

·
Registered
Joined
·
11,157 Posts
Ok, my next question. Can both "services" share the 2 required ground rods with a #6 solid?
1 drop = 1 service, no matter how many meters are on it.
 