2 Posts
Discussion Starter · #1 ·
Before anyone asks I am a qualified spark.. been off the tools for years and getting back into it..
In regards to EICR’s it’s been a while..
Acceptable to add R1 R2 to Ze for ZS or do you all test all 3 anyway? I know it’s not acceptable to ZS and take off ZE to get R1 R2..
Thanks
 

·
Big nosed attic troll
Joined
·
10,371 Posts
Before anyone asks I am a qualified spark.. been off the tools for years and getting back into it..
In regards to EICR’s it’s been a while..
Acceptable to add R1 R2 to Ze for ZS or do you all test all 3 anyway? I know it’s not acceptable to ZS and take off ZE to get R1 R2..
Thanks
test all 3 anyway but ya u can add r1+r2 to the ze to get the zs
 

·
Band Member
DIYer Extrodinaire
Joined
·
8,242 Posts
My Ohm chart only has R 😢
 

·
Big nosed attic troll
Joined
·
10,371 Posts
Before anyone asks I am a qualified spark.. been off the tools for years and getting back into it..
In regards to EICR’s it’s been a while..
Acceptable to add R1 R2 to Ze for ZS or do you all test all 3 anyway? I know it’s not acceptable to ZS and take off ZE to get R1 R2..
Thanks
 

·