I have zero experience with those chargers.Does an EV charging station outlet require a disconnect or does the breaker itself count as the disconnect?
625.23 Disconnecting Means. For electric vehicle supply equipment rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. The disconnecting means shall be capable of being locked in the open position.Anything under 50A does not require a disconnect, if it's 240v 60A and up a disconnect must be installed as per article 625 of NEC
Do these chargers output AC or DC? Could they be talking about output ratings?625.23 Disconnecting Means. For electric vehicle supply equipment rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. The disconnecting means shall be capable of being locked in the open position.
That's interesting wording. Note the "more than" in two locations in the sentence, and that the voltage reference point is ground, not across phases.
So a 60 amp, 240v charger does not need a disconnecting means. It's not "more than 60 amps", and is not "more than 150 volts to ground".
You can almost guarantee this one is misinterpreted by inspectors all over.
Do chargers usually have a reference to ground?8V71 said:Do these chargers output AC or DC? Could they be talking about output ratings?
I don't know anything about these. DC out or just AC to a charger installed in the vehicle?Do chargers usually have a reference to ground?
Yea that pretty much answered my question. Haven't had much experience with chargers or DC. I think it would be pretty unlikely to have 150+ dc on these chargers. Maybe that code is for "quick" chargers that use 600y or 480y systems. I.e commercial applications8V71 said:I don't know anything about these. DC out or just AC to a charger installed in the vehicle? I'm pretty sure the negative on a regular automotive battery charger is bonded to the AC ground if that's what you mean.
Yes... read through the 2008 article just this week and saw this. Does seem to be for commercial installations 277v or more or more than 60A.625.23 Disconnecting Means. For electric vehicle supply equipment rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. The disconnecting means shall be capable of being locked in the open position.