Im wiring an elevator in a residence, Threes phase 120/208. A 60 amp breaker feeds a heavy duty siemens disconnect on the fourth floor. the load side of that disconnect goes to another heavy duty disconnect in the top of the shaft. I need to install contacts so that a battery backup system will be able to raise or lower the car incase of loss of power. im a journeyman, though i have never run into this and am on my own can anyone offer a little guidence?
 

· Senior Member
Joined
·
415 Posts
Is this a new install? If so then a link to the manufacturer's website would help us understand what you have.
Are the elevator motors 208V 3 phase?
And the battery supply will have an inverter to produce 208V 3 phase?
 

· Registered
Joined
·
421 Posts
You need a axillary contact in both disconnects, with 2 conductors, in series, if one or the other disconnect is open it will take the elevator out of emergency mode. Your SH who sold you the disconnect should be able to get them. If not GE has them for their equipment.
 

· Registered
Joined
·
2 Posts
Discussion Starter · #5 ·
RHWilks said:
You need a axillary contact in both disconnects, with 2 conductors, in series, if one or the other disconnect is open it will take the elevator out of emergency mode. Your SH who sold you the disconnect should be able to get them. If not GE has them for their equipment.
Ok, it's a Siemens heavy duty disconnect, I have the contact kits with one set of each NO and NC contacts. They install with 10-32s on the handle. I have the 24 vdc wires in the shaft disconnect that the elevator guy already ran. I think I need an 18-2 from one disconnect to the other wired normally open, right? One wire gets tied straight throu and the other goes through both normally open contacts?
 

· Registered
Joined
·
421 Posts
Depending on the elevator. Last one I did it was open when the disconnect was open, closed when ect... it must open or close the circuit when the disconnect is off. The battery back up is in the event of a power failure. Not opening the disconnect for maintenance.
 

· Registered
Joined
·
1,138 Posts
Is it a hydraulic elevator?
If so, the ups gets wired into the controller and if there is a power loss and all disconnects are in the on position, then the controller uses the UPS power to allow gravity to lower the car.
As far as the NO or NC contacts usually the elevator guys want the contacts closed for normal operation.
 

· Registered
Elevator Industry
Joined
·
14 Posts
Is the battery backup system compatible with the elevator control system? more details are required as each controller may require a different configuration of automatic return device.

There are many types of battery backup system for elevators like:
1. DC supply to the drive DC bus + some sort of feeding the controller with power.
2. AC single phase to the controller.
3. AC three phase to the controller.
4. Act like controller to drive the machine and monitor the safety circuit.
 

· Moderator
Retired
Joined
·
18,866 Posts
Is the battery backup system compatible with the elevator control system? more details are required as each controller may require a different configuration of automatic return device.

There are many types of battery backup system for elevators like:
1. DC supply to the drive DC bus + some sort of feeding the controller with power.
2. AC single phase to the controller.
3. AC three phase to the controller.
4. Act like controller to drive the machine and monitor the safety circuit.
This one 9 years old.
 