Discussion Starter · #1 ·
Elevator sales man said we do not need a elevator recall because the elevator opens to the same lobby. But I cannot find an exception for not having the recall anywhere. Any help would be appreciated.

2 story office building, type b construction, sprinkle, no fire alarm, elevator stops at 2 floors, travels less than less than 25 ft, elevator is NOT a means of egress, doors open to the same "air" (main lobby is 2 stories high)
 

·
Registered
Retired Elevtor Constructor, Sales, Adjuster. NEIP Certified Inspector
Joined
·
1 Posts
Elevator sales man said we do not need a elevator recall because the elevator opens to the same lobby. But I cannot find an exception for not having the recall anywhere. Any help would be appreciated.

2 story office building, type b construction, sprinkle, no fire alarm, elevator stops at 2 floors, travels less than less than 25 ft, elevator is NOT a means of egress, doors open to the same "air" (main lobby is 2 stories high)
Salesmen are usually only marginally aware of any codes. Call a certified inspector to get your answer correctly. None of us charges for a simple question.
 