Can't speak to New York code but the IBC requires 1 foot-candle measured at the floor level in the egress pathway.

Pete
 

· Registered
Joined
·
1,576 Posts
Discussion Starter · #4 ·
I'm doing an LED rertro fit. Each floor in the hallway had every other fixture as an EM. Since we eliminated all the ballasts I needed to install EM wall packs. I spoke to an engineer today and he expressed that a EM light is need every 25'. But, couldn't clarify if it was a federal or state requirement. Since this job is under HUD jurisdiction.
 

· Registered
Joined
·
654 Posts
Not sure if this was adopted or not, but it at least gives a detailed description:

1006.2 Illumination level.
The means of egress illumination level shall not be less than [2 foot-candles (22 lux) at the floor level in exits, at exit discharges, and in public corridors, and shall not be less than 1 foot-candle (11 lux) at the floor level in exit access components other than public corridors] 1 foot-candle (11 lux) at the walking surface level.

http://www.nyc.gov/html/dob/downloads/pdf/ll47of2010.pdf
Note the exceptions, though. The requirements may be completely different for dwelling units and sleeping units in Groups I-1, R-1, R-2 and R-3.
 