Are you tapping a feeder or service conductors?
A feeder SHOULD have a ground.
A feeder SHOULD have a ground.
what do you mean by the "primary and secondary grounds"? Never heard this terminology.... The Main panel is completely full, no room for a two-pole, this is the reason I'm tapping off the Feeder. I'm thinking I need to bond the nuetral to the can, like the Main, to ensure a path for objectionable current. btw...there is no AHJ in this area.I'd put a two-pole in the existing panel and do a four wire sub feed to a sub panel. I think checking with the AHJ is a good idea, but I also think if the 200 amp panel has a valid primary and secondary grounding wire, I think a sub panel would be appropriate.
I have never run into the setup you describe. Does the main disconnect have the primary and secondary grounds in it or are they at the panel and is the panel a main lug only or does it have a main breaker?
So install a sub-panel right next to the main and move some of the lesser circuits over to the sub to make room. :whistling2:The Main panel is completely full, no room for a two-pole, this is the reason I'm tapping off the Feeder.
Not with a sub-panel you don't. You MUST run a 4-wire feeder (in most cases, and all cases within the same structure) to a non-service panel (sub-panel). Neutrals and grounds are kept isolated.I'm thinking I need to bond the nuetral to the can, like the Main, to ensure a path for objectionable current.