Helping a friend wire up his 3 car detached garage and he fail inspection today.

First, panel too far from ufer ground!
Panel is on one side of garage and the ufer is on the other side, 30 ' away.

Any problem with that?

60 amp breaker feeding 100 amp main.

Gc was present for inspection and called him.
Inspector left his card and the paperwork.

Any code issues with this two items?
 

·
Registered
Joined
·
656 Posts
The grounding electrode may be an issue because it's not 'as close as practicable' to the service disconnect, but I'm not sure if that requirement is actually anywhere in Article 250.

The 100A fed from the 60A should be fine as long as the feeder is sized for 60A.
 

·
Registered
Electrician
Joined
·
3,668 Posts
Discussion Starter · #3 ·
The grounding electrode may be an issue because it's not 'as close as practicable' to the service disconnect, but I'm not sure if that requirement is actually anywhere in Article 250.

The 100A fed from the 60A should be fine as long as the feeder is sized for 60A.
Fed with #6
 

·
Registered
Joined
·
656 Posts
Copper, I assume? There is nothing wrong with that. The 100A MCB in the sub-panel is simply acting as a disconnect, not an OCPD. The panel could be MLO with 100A or 225A bussing also, and there's no violation with that, either.
 

·
Electrical Simpleton
Joined
·
3,350 Posts
FWIW, I know of no distance limitation for a GEC.

And it sounds as if the feeder is good also.

Did the inspector cite any code sections?

Pete
 

·
ET rocks
Joined
·
2,875 Posts
jb, what's the diff. when they make you guys run an EGC to timbuktoo to hit the water pipe?

Secondly, this inspector has dyslexia when it comes to downstream panels and feeders.

i call BS. His paperwork should have listed specific code articles for the fail.(beat ya to it, Ken.)
 

·
Registered
Electrician
Joined
·
3,668 Posts
Discussion Starter · #9 ·
I asked if any code sections were listed, but he hasn't seen the paperwork yet.

I told him as far a I knew, no violations existed, but I wanted to make sure.

Since he as the homeowner did the work, how should he approach the inspector without seeming to be a ****?
 

·
ET rocks
Joined
·
2,875 Posts
I asked if any code sections were listed, but he hasn't seen the paperwork yet.

I told him as far a I knew, no violations existed, but I wanted to make sure.

Since he as the homeowner did the work, how should he approach the inspector without seeming to be a ****?
Sorry man, but this one's on you. It's all part of the buddy deal. Call up the inspector and diplomatically get er taken care of.:thumbsup:
 

·
Registered
Electrician
Joined
·
3,668 Posts
Discussion Starter · #13 ·
Ok, here is the deal.

1-#6 wire is not rated for 100 amps.
2-Needed to see breaker feeding panel.
3-Needed grounding rod on same side of garage as panel. Ground wire needs to be minimum#6 solid awg.

Right now we have #10 running from panel to ufer.

Do we need #6?
! know we do not need the rod, but may put it in anyway.
 

·
ET rocks
Joined
·
2,875 Posts
Yeah, he just needed to verify the OCD ahead of the feeder.

Table 250.66 gives #8 cu minimum for a GEC. (get rid of the 10)

i'm not aware of the requirement to have a rod, if your electrode is a ufer.

Maybe the rod and #6 is a local amend.? (doubt it tho)
 

·
Registered
Joined
·
11,105 Posts
For what reason was the panel not located near the UFER?
 

·
Registered
Electrician
Joined
·
3,668 Posts
Discussion Starter · #16 ·
A resolution has been reached.

Remove the wire to the ufer, install a ground rod and use the #10 from the panel to the rod.

Make sure to use a 60 amp breaker to feed the garage with.
 

·
Registered
Electrician
Joined
·
3,668 Posts
Discussion Starter · #19 ·
Trading in a Ufer for a Grod Jb?

thats just not right....

~CS~
I agree, but the inspector was worried about the length of wire in case of a lightning strike!

As least he didn't say anything about tripping breakers.:jester:
 