I'm installing a hot-tub 60A GFCI box for an outdoor hot-tub. This line runs back to the sub-panel, where I need to install a Federal Pacific 60A breaker. (yes 60A!, according to AcuraSpa specs)


My question is as an electrician how do you guys approach the liability issue of installing a new F.P. breaker when the hype out there is so confusing.

I'd like to just take a quick check of each breaker for contact condition and if ok install the new 60A breaker. But then I feel Liable if something goes wrong.

The real kicker is that the 1983 United States Consumer Product Safety Commission (last edited 2011) did not reach a consensus with regard to federal pacific panel safety. One would think that with such an important safety issue a unanimous decision is the only way to go for an electrician to feel safe enough that liability was not a concern.

http://www.cpsc.gov/en/Newsroom/News-Releases/1983/Commission-Closes-Investigation-Of-FPE-Circuit-Breakers-And-Provides-Safety-Information-For-Consumers/

I've read other posts though that say federal pacific since the early 80s' had no problems and were just fine, that they installed the breaker and just moved on.

Any thoughts/ideas?
 

·
Retired Account
Joined
·
39,697 Posts
What do you care if they power their residence with fireflies as long as the powers that be sanction it onilozay ?

They make aftermarket stab lock fpe replacements btw

Those are also sanctioned 'safe'

~CS~
 

·
Retired Account
Joined
·
39,697 Posts
I checked that article, well written. I guess the best option I've read is to inform the home-owner without fear tactics and then put the decision in their hands
I've done that myself btw

bottom line, if they were all that bad, the CSPC would have had a recall

the state inspectors will be reduced to informing them of the same

iirc, save for a few double pole fpe's , they didn't

~CS~
 

·
Donuts > Fried Eggs
Joined
·
17,042 Posts
Frankly, I've changed my mind on on FPE because of talking to people who've tested them and running small scale test of my own.

I believe they probably did have the issue that CPSC said they did on very specific model breakers. But as far as the remaining ones I don't' think there is a problem built into the breakers themselves. I think they should be swapped because their age makes them unreliable, but I think that's true of all breakers of that vintage.
 

·
NJ-IEC
Joined
·
14,387 Posts
I'm installing a hot-tub 60A GFCI box for an outdoor hot-tub. This line runs back to the sub-panel, where I need to install a Federal Pacific 60A breaker. (yes 60A!, according to AcuraSpa specs)


My question is as an electrician how do you guys approach the liability issue of installing a new F.P. breaker when the hype out there is so confusing.

I'd like to just take a quick check of each breaker for contact condition and if ok install the new 60A breaker. But then I feel Liable if something goes wrong.

The real kicker is that the 1983 United States Consumer Product Safety Commission (last edited 2011) did not reach a consensus with regard to federal pacific panel safety. One would think that with such an important safety issue a unanimous decision is the only way to go for an electrician to feel safe enough that liability was not a concern.

http://www.cpsc.gov/en/Newsroom/News-Releases/1983/Commission-Closes-Investigation-Of-FPE-Circuit-Breakers-And-Provides-Safety-Information-For-Consumers/

I've read other posts though that say federal pacific since the early 80s' had no problems and were just fine, that they installed the breaker and just moved on.

Any thoughts/ideas?


My thought is this.... these people can afford to install a new jacuzzi but not to replace a Federal Pacific panel? Not my kind of customer. Change out that panel and then install the new equipment.
 

·
Registered
Joined
·
1,460 Posts

·
NJ-IEC
Joined
·
14,387 Posts
How do figure that he is not an electrician? He asked a legitimate question.

Because the majority of electricians know the dangers of Federal Pacific Electric equipment. That's why.

Federal Pacific Circuit Breakers: Investigation Finds Decades of Danger

Linky-link here

If your home was built before 1990, it may have a faulty Federal Pacific circuit breaker and could be a fire risk. It’s a fact that been known for years, but there has never been a recall.

The “Stab-Lok” circuit breaker and panel produced by Federal Pacific Electric (FPE) installed in hundreds of thousands of homes in the Bay Area may cause house fires, according decades of documentation and electrical experts interviewed by the NBC Bay Area Investigative Unit. Stab-Lok circuit breakers are most commonly found in houses built before 1990.

Click here to see how to determine if your home has a Federal Pacific Stab-Lok circuit breaker.

Information and lab tests uncovered by the NBC Bay Area Investigative Unit show many Federal Pacific Electric Stab-Lok breakers will not trip, continuously providing electricity to the short circuit, which can cause intense heat and in some cases fire. When working properly, circuit breakers are designed to prevent fires. They are designed to cut off the flow of electricity when charged with excessive electrical demand or short circuit, also known as “arching.”

“There is no inconsistency and no dispute in the fact that they are defective,” says Jesse Aronstein, an engineer, who has spent more than 20 years researching FPE Circuit Breakers.
Aronstein has testified in lawsuits against FPE and warned, “The breaker is a safety device that is supposed to prevent fires, if it doesn’t work as required, you get an increased risk of fire.”

NBC Bay Area spoke with a Bay Area attorney representing Federal Pacific and she declined to comment on the information included in this investigation.

The Investigative Unit asked how did a defective product meant to provide safety, get into millions of homes? And how can a defective circuit breaker pass federal inspection plus get the UL stamp of approval? According to Aronstein, the answer is simple. He says the company cheated. “FPE was cheating on the testing and applying the label to a product that was defective and did not meet the requirements,” Aronstein claims.

His allegation is supported by this document obtained by NBC Bay Area. The 1982 Securities and Exchange Commission filing by Reliance Electric, the company that purchased FPE says, “UL listings on circuit breakers made by Federal Pacific have previously been obtained through the use of deceptive and improper practices.”

Aronstein told NBC Bay Area the deceptive and improper practices included tricking UL inspectors by using a hidden remote control to force the breaker to trip if it was not tripping properly.

After years of researching the issues with Federal Pacific circuit breakers, Aronstein believes they are responsible for approximately 2,000 fires nationwide each year.

Investigative Reporter Tony Kovaleski also interviewed Bay Area electrical contractors and engineers. Geoff Williams is a master electrician, who has replaced Stab-Lok electrical breaker panels in Bay Area homes and businesses for decades. Williams says his personal experience is consistent with Aronstein’s testimony.

Williams says he has witnessed Federal Pacific Stab-Lok failures on multiple job sites. “I’ve seen so many places burned by these panels,” said Williams. “It’s frightening to me every time I see it.”
Williams recalled a morning in 1979, he says he nearly lost his life in a crawl space under a Bay Area house. Williams said that as he approached a circuit breaker panel, “It lit up cherry red. It lit up that crawl space like the gates of hell. It could have killed me.”

Williams says it was an FPE Stab-Lok panel. “I had to role and approach that panel through a small opening through the crawl space and shut it off manually.” He added, “With the fire shooting flames at my face.”

NBC Bay Area had FPE Stab-Lok circuit breakers tested at the Berkeley Research Company. Bernard Cuzzillo has a Ph. D. in electrical engineering, is a fire specialist and owns BRC. Cuzzillo tested a dual pole 60 amp breaker, similar to the ones tested by Underwriter Laboratories and to the ones found in homes in the Bay Area.

To test the circuit breaker, he forced double the electrical current it’s capable of handling and timed it. Cuzzillo says if working properly the Federal Pacific circuit breaker should have tripped in less than two minutes. At one minute ten seconds, Kovaleski noted smoke coming out of the breaker.

Kovaleski and Cuzzillo watched the circuit breaker smoke for more than four minutes. “It’s smoking and it hasn’t tripped. Why not?” asked Kovaleski. “Because the mechanical mechanism that is supposed to be tripping the mechanism is stuck,” replied Cuzzillo. The expert says, therein lies the problem with FPE Stab-Loks.


NBC Bay Area also uncovered documents reporting other FPE equipment that did not work properly. This internal document from Bay Area Rapid Transit from 2008 says BART had electrical equipment problems with Federal Pacific products.

It reads, "There have been two instances of failures with the old Federal Pacific Electric secondary distribution panel. Failure of this old equipment has caused delays to BART train service and created potentially unsafe conditions."

In the small town of El Sobrante just north of Berkeley, NBC Bay Area spoke with retired electrician and homeowner Daniel Schmidt. Schmidt decided to remove his Federal Pacific Stab-Lok panel. Years of electrical work taught him that if he ignores FPE’s history, the inevitable might happen. “It’s a panel that’s got quite a reputation,” he said.

Schmidt lives in the home with his wife and two dogs. They’ve also raised two boys in El Sobrante.
A new electrical system removes a lingering issue from their lives, but more importantly, the investment also brings security. “I know it’s going to be safer,” he added.

The Federal Pacific Electric company no longer exists but experts estimate millions of defective circuit breakers it manufactured remain in homes all over the country. Published reports show not every Federal Pacific circuit breaker is defective. In the wake of the controversy, Underwriters Laboratories (UL) removed the U-L listing for the breakers, but not before millions were sold and installed in homes built from the 1950s to the 1980s.

In recent years, some of the breakers have been modified and did pass U-L inspection.

The Consumer Product Safety Commission did conduct additional testing of the Federal Pacific circuit breakers in the 1980s. Controversy and legal challenges followed the testing. Many called on the CPSC to recall the breakers, but they were never recalled. Some experts have said the CPSC did not recall the Federal Pacific circuit breakers because it did not have the budget to battle a possible legal fight from Federal Pacific’s then-parent company.


If you have witnessed a problem with Federal Pacific circuit breakers, the Consumer Product Safety Commission asks that you file a report at www.saferproducts.gov.
 

·
Registered
Joined
·
2,325 Posts
I wouldn't be so quick to hang my hat on an NBC News article. How much advertising would they garner if the article cited the fact that CPSC reopened the case and determined in 2011 that there still was insufficient evidence that the breakers posed a danger?

http://inspectapedia.com/fpe/FPE_CPSC_2011.pdf

Danger and death sell air time, and you can't scare Mr. and Mrs. Homeowner if you don't tell them the panel might be iffy.

The "evidence" presented in the NBC article has a Ph D. testing ONE breaker. Who can't find a defective 30 year old breaker of any brand?

I wouldn't blame anyone for being sceptical of the entire situation. It's certainly not a slam dunk and the OP is right to question it.

NBC should have recommended testing and/or replacing any 30 year old breakers, not just FPE.
 

·
Registered
Joined
·
1,135 Posts
My thought is this.... these people can afford to install a new jacuzzi but not to replace a Federal Pacific panel? Not my kind of customer. Change out that panel and then install the new equipment.
I've made that decision. When asked to do something and there's is an FPE panel, I just say that I won't come out of it. The same way as how I won't touch K&T anymore. If they don't want to pay to clean that crap out and install new, safe, up-to-date hardware, they can call someone else to play with their old crap.
 

·
Registered
Joined
·
1,460 Posts
I have seen a whole bunch of Federal panels and breakers in great shape. I am little skeptical too. I am also skeptical about aluminum wiring but that is another topic beat to death. I don't see a problem with putting a new reconditioned breaker in a federal panel. I guess the only concern I do have is that if something goes wrong down the line,I probably would have been the last one working in the panel and the lawyers and insurance companies will probably point the finger at me.
 

·
Registered
Joined
·
1,135 Posts
I have seen a whole bunch of Federal panels and breakers in great shape. I am little skeptical too. I am also skeptical about aluminum wiring but that is another topic beat to death. I don't see a problem with putting a new reconditioned breaker in a federal panel. I guess the only concern I do have is that if something goes wrong down the line,I probably would have been the last one working in the panel and the lawyers and insurance companies will probably point the finger at me.
Not only that, but you could make more money by replacing the panel :thumbup:

It's easy to sell panel change outs when they have FPE panels, just tell them to Google "Federal Pacific" for themselves and read about it and look at the hundreds of pictures of burnt down houses :laughing:
 