Have you ever read 250.118?I am bidding on a couple of panel changes. - The first panel is fed from a 200A disconnect; the feeders are run in metal conduit with no equipment ground conductor. It seems to me that there might be an exception that allows this in an existing installation. (I want to leave the feeders alone in possible. It is a long run and I am trying to keep costs down... Maybe I should just plan on replacing them, but anyway:whistling2Any ideas here? I think the metal conduit is the EGC but not completely sure that is okay... something new or unfamiliar every day!
Thanks Roger, I remember now the electrical inspector here telling me the pipe is considered the EGC for another installation. That was a while ago though... I had forgotten about it.Have you ever read 250.118?
Roger
I have seen a lot more loose EMT compression couplings and connectors than I have set screw ones.Its not my preferred way of doing things if the metal conduit is emt with set screw couplings and connectors although its allowed. We've all seen set screw fittings that are loose or have come open.
I have zero worries about it when its threaded rigid conduit however.
That rigid conduit would surely carry more fault current than a #6 wire in the case of a serious fault:laughing:
All so true don......although personally......I have seen more set screw stuff loose. I guess its like you said.....a hack install is a hack install.:thumbsup:I have seen a lot more loose EMT compression couplings and connectors than I have set screw ones.
I have seen more than one rigid conduit run where the couplings were not made up tight and a fault blew holes in the threads at a number of couplings in the run.
I have also seen a lot of green wires that were not properly terminated.
A poor installation can be made no matter what the product is.
If the portion of the conduit system seems to be installed correctly it probably is okay to be the EGC. Measure from point A to B to C and read the resistance.I am bidding on a couple of panel changes. - The first panel is fed from a 200A disconnect; the feeders are run in metal conduit with no equipment ground conductor. It seems to me that there might be an exception that allows this in an existing installation. (I want to leave the feeders alone in possible. It is a long run and I am trying to keep costs down... Maybe I should just plan on replacing them, but anyway:whistling2Any ideas here? I think the metal conduit is the EGC but not completely sure that is okay... something new or unfamiliar every day!
Honestly, I'm not sure. When I was there looking at the whole thing I let the customer know I didn't want to take it apart or mess with it at that point. I was not charging her for the estimate. On a free estimate I am really hesitant to take even the covers off some of that old service equipment... you know that stuff can just fall apart on you and then you got something you have to deal with and nobody has signed or agreed to pay you anything. It was in a marshy area too.... I don't know who decided to put the service equipment right next to a wetland conservation area, but whatever.where is the service grounded? from the panel, or the disconnect?
I am not sure who you are asking but I will weigh in. The service is GROUNDED by virtue of running a conductor from the neutral buss of the panel to an electrode in intimate contact with Mother Earth.where is the service grounded? from the panel, or the disconnect?
... made me laugh.and that contact isnt always so intimate:whistling2:
As far as ground rods are concerned tell me what you think that the word INTIMATE means.and that contact isnt always so intimate:whistling2:
After the first fault it is all welded together and I have seen that a few times.All so true don......although personally......I have seen more set screw stuff loose. I guess its like you said.....a hack install is a hack install.:thumbsup: