My jerk boss sent me out to this job in a very large facility with around 30 panels and probably over 1000 breakers. I'd say around 4 acres with panels everywhere. 24/7 facility. I have to fix a couple outlets and a couple 277v lights. I have no idea which panel or breaker they come from. Nothing is labeled at all. I tried my 61-958 ideal tracer and it did not work. My boss said to just short it out. Any other ideas?
 

· Registered
Joined
·
1,827 Posts
My jerk boss sent me out to this job in a very large facility with around 30 panels and probably over 1000 breakers. I'd say around 4 acres with panels everywhere. 24/7 facility. I have to fix a couple outlets and a couple 277v lights. I have no idea which panel or breaker they come from. Nothing is labeled at all. I tried my 61-958 ideal tracer and it did not work. My boss said to just short it out. Any other ideas?
I have put a certain amp load on something and find it that way if possible. Short it out and what you still have to LOTO the circuit so it's safe to work on.
 

· Senile Member
I make all the electrons line up for their Flu shots
Joined
·
37,505 Posts
Don't short anything out. There are better ways to find it. Have you got a helper? Plug in a whole hog and have him repeatedly pull the trigger while you amp check all the circuits till you find the one that swings the "needle". You could do the same thing for the lighting circuits by flipping the switch on and off the same way while you find the breaker. Don't forget to put on your space suit to work around that open panel.........:whistling2:
 
  • Like
Reactions: owl

· RIP 1959-2015
Joined
·
39,532 Posts
My jerk boss sent me out to this job in a very large facility with around 30 panels and probably over 1000 breakers. I'd say around 4 acres with panels everywhere. 24/7 facility. I have to fix a couple outlets and a couple 277v lights. I have no idea which panel or breaker they come from. Nothing is labeled at all. I tried my 61-958 ideal tracer and it did not work. My boss said to just short it out. Any other ideas?
Do not short out any thing , you could dump the whole building and your boss will get his head handed to him, this is not the old days and he could get sued big for that.

What Macmikeman said is the way to go..:thumbsup:
 

· Registered
Joined
·
33,810 Posts
Seems your boss is not a jerk he has you working.

I use to utilized a lamp flasher and look with an amp clamp for pulsating current. If you used a large enough load and were able to turn the load on and off you could locate the CBs

It can be done apply your trade and professionalism.
 

· Registered
Joined
·
14,602 Posts
The ideal is the only tracer I've ever had any luck with in large buildings. I got real turned off of tracers by amprobes that never seemed to get it right but the ideal is awesome.

How are you hooking the transmitter to the circuit you are trying to trace?
 

· Banned
Joined
·
89 Posts
Discussion Starter · #14 ·
Follow the conduit back to get you in the general area and narrow it down? Work on it live?
won't work on both

Are you adjusting the sensitivity? My 958 has never let me down, as long as I find the right panel. Maybe there is one you haven't found yet?
yes. some of the readings are so close i am leary of flipping breakers as we might shut down the wrong items which would be a disaster here

Seems your boss is not a jerk he has you working.

I use to utilized a lamp flasher and look with an amp clamp for pulsating current. If you used a large enough load and were able to turn the load on and off you could locate the CBs

It can be done apply your trade and professionalism.
that may work but I would have to clamp on 1000 different breakers over a 4 acre facility

The ideal is the only tracer I've ever had any luck with in large buildings. I got real turned off of tracers by amprobes that never seemed to get it right but the ideal is awesome.

How are you hooking the transmitter to the circuit you are trying to trace?
the correct way I think. Clipping on the open lead of hot and a separate neutral with 25ft cord
 

· Registered
Joined
·
439 Posts
Chances are highly likely that the panel you want is close to the offending issue. Places don't normally spend more money than they must, and long wire + long conduit + long labor hours = excess money. You can usually eliminate 800 breakers of your thousand.

Start at the closest panel that has the correct voltage and configuration.
 

· Donuts > Fried Eggs
Joined
·
17,035 Posts
Don't short things out: No guarantee you'll be able to find it even after you short it out, and now they don't have power. Then you're really screwed. Also, at 277 you might dump a much larger breaker upstream.

I agree the flasher trick can work great. I used to have a super-sized version I made out of a 1kW heating element and a multi-tap transformer. You can find a lot of stuff at a variety of voltages.
 