Depending on the specifications, usually, conduit is run with flex drops to the devices on the T-bar or in the walls, but as you can see, CEC allows a variety of methodsI'm looking to install a new strobe to an existing supervised FA system and I noticed that some of them are connected with conduit and some used BX. I was under the impression one cannot use anything else but conduit. What's your opinion guys?
32-102
32-102 Wiring method
32-102
(1) ∆ All conductors of a fire alarm system shall be
(e) installed in metal raceway of the totally enclosed type;
(f) incorporated in a cable having a metal armour or sheath;
(g) installed in rigid non-metallic conduit; or
(h) installed in electrical non-metallic tubing.
(2) Notwithstanding Subrule (1), conductors installed in buildings of combustible construction in accordance with the Rules of Section 12 shall be permitted to be
(a) non-metallic-sheathed cable;
(b) fire alarm and signal cable; or
(c) installed in a totally enclosed non-metallic raceway.