Just fired up a service today for a Bitcoin mining operation. What a fiasco. Originally it was going to be 7.5 kW of load. Then they decided to move to his garage: an old single level house with an ancient 100 amp service. 25 kVA transformer feeding 4 houses. The guy upped his consumption to 28.8 kW. Getting the PoCo to change the transformer was something special. They kept insisting that the 25 kVA transformer would handle it due to "diversified loading". I finally got through to them that this guy was going to be pulling 120 amps 24/7 365, no diversity... real amps.
"So... wait... you're saying there will be 120 amps continuous... all the time?"
They wanted to put in a 37.5 kVA pole pig... which would leave just 36.25 amps for all 4 houses to share. We finally talked them into a 50 kVA... So the house gets a 320 amp service, with the old 100 amp panel remaining and a new 200 amp bolt-on panelboard for his servers. I'm excited to see where this goes. I expect he's going to outgrow his little neighborhood single phase primary soon.
"So... wait... you're saying there will be 120 amps continuous... all the time?"
They wanted to put in a 37.5 kVA pole pig... which would leave just 36.25 amps for all 4 houses to share. We finally talked them into a 50 kVA... So the house gets a 320 amp service, with the old 100 amp panel remaining and a new 200 amp bolt-on panelboard for his servers. I'm excited to see where this goes. I expect he's going to outgrow his little neighborhood single phase primary soon.