I'm looking for ideas to solve a problem. I have an installation where the measured foot candles are lower than the computer models. 3 computer models using 2 different programs show approximately 40% more foot candles than 3 different foot candle meters are showing.
So far, 2 different electrical contractors and the electrical engineer have looked at the install and found no issues. Measured voltage at panels and fixtures are well within tolerance for the ballasts, voltage drop is almost non existent, the building is served by it's own POCO transformer, there are probably 200 fluorescent fixtures on the 277 system, and maybe 50 computers on the 120 side, each circuit is a dedicated neutral, so I can't imagine a harmonic issue.
I'm looking for ideas on what the problem is. I think we have eliminated: voltage, neutrals, temperatures, surface reflectivity, and mounting heights as possible causes. I'm willing to entertain just about any theory at this point.
So far, 2 different electrical contractors and the electrical engineer have looked at the install and found no issues. Measured voltage at panels and fixtures are well within tolerance for the ballasts, voltage drop is almost non existent, the building is served by it's own POCO transformer, there are probably 200 fluorescent fixtures on the 277 system, and maybe 50 computers on the 120 side, each circuit is a dedicated neutral, so I can't imagine a harmonic issue.